Just wired a kitchen extension from an existing dual rcd 17th edition consumer unit. There are 3 new circuits to the CU, ring main, lights and cooker.
With my old company I would inspect and test the whole consumer unit, ie all the old circuits and the 3 new ones. The Schedule of test results would be labelled, for example, circuit 1 to 8 with a full set of results for the whole installation.
My new company say this is wrong and all I have to do is test the 3 circuits I have done. So 1 to 5 on the schedule of test results would be blank and way 6, 7, and 8 would have all the results written in.
Obviously in both scenarios RCD and Ze etc would be tested.
Which way is correct?
 
An electrical installation cert only covers the work you have carried out which in this case would be your 3 new circuits.

In the extent covered box you only describe the work you have done as this is what the cert applies to, you can't certify work you haven't personally carried out.
There's nothing essentially wrong with testing everything, commendable even, but the cert would still only apply to your 3 new circuits. The extra time taken to test the existing circuits plus leaving yourself open to question should anything happen with one of the existing circuits is probably what your company is concerned about.

In this day & age with the blame culture we live in, you need to make sure your own --- is 100% covered.
 

Reply to Electrical Installation Certs. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
Thanks for the advice, I actually had no idea about the HMO licensing rules so have learnt a lot. Just did a search, its not licensed as an HMO...
Replies
5
Views
394

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top