electrical installation farm | on ElectriciansForums

Discuss electrical installation farm in the UK Electrical Forum area at ElectriciansForums.net

Joined
Feb 11, 2018
Messages
169
Reaction score
30
Location
scotland
Hi there iam about to start a new installation removing existing electrical equipment from a farm and renewing every board etc, inside the new distribution boards my question is would i have a 300mA RCD main switch there for outgoing circuits I.E sockets on a 30mA rcbo.? Also regulation 705.415.2.1 intended for live stock all supplementary bonding shall be connected to extraneous conductive parts sizing of supplementary bonding for this? thanks in advance dont really do farms first one i will do with my boss just want a bit knowledge and hope iam not being stupid asking these questions
 
You only need to protect livestock where livestock might be present. So within office/accommodation areas you only need to provide additional protection as per the book.

Farms can be notoriously difficult to design due to their completely random layouts and multiple uses of buildings. They key is to get your distribution circuits right the first time and add plenty of room for future expansion.

Farmers will quite happily add loads to their installation without a second thought then blame you when the whole lot falls over just at the wrong time.
 
You only need to protect livestock where livestock might be present. So within office/accommodation areas you only need to provide additional protection as per the book.

Farms can be notoriously difficult to design due to their completely random layouts and multiple uses of buildings. They key is to get your distribution circuits right the first time and add plenty of room for future expansion.

Farmers will quite happily add loads to their installation without a second thought then blame you when the whole lot falls over just at the wrong time.
total agree with that mate hear alot about farmers as for office/accommodation there is none on this install just farm land there is a shed with a lot of live stock in a farm shed which will need bonding because they can actually touch the metal work
 
Also regulation 705.415.2.1 intended for live stock all supplementary bonding shall be connected to extraneous conductive parts sizing of supplementary bonding for this?
To check you caught the point - that bit is about connecting exposed and extraneous conductive parts together in areas that can be touched by livestock.
Regarding the size, see section 544.2.2 - you will see why a one size fits all answer isn't possible!
 
Hi there iam about to start a new installation removing existing electrical equipment from a farm and renewing every board etc, inside the new distribution boards my question is would i have a 300mA RCD main switch there for outgoing circuits I.E sockets on a 30mA rcbo.? Also regulation 705.415.2.1 intended for live stock all supplementary bonding shall be connected to extraneous conductive parts sizing of supplementary bonding for this? thanks in advance dont really do farms first one i will do with my boss just want a bit knowledge and hope iam not being stupid asking these questions
Time delay Rcd upfront
 
Section 705 has most details.

As above, most areas will need a 100mA or 300mA delay RCD as part of fire protection.

Also note the extra bonding, earth mats, etc, in any areas with livestock and special needs if the supply is PME (TN-C-S). In that case (even for TN-S in case it is "upgraded" to TN-C-S) you might find it simpler to TT the installation with the up-front delay RCDs along with RCBOs for selectivity and adequate earth rods, the usual spec is 167 ohm for 300mA but aim for under quarter that as you want no more than 25V at disconnection and margin for drought/frost taking the top 0.5-1m of rod out of commission.

Also remember rats! A sparky I know who does a lot of farm work swears by Flexishield cable for most stuff that does not merit SWA. It is tough, UV resistant, gland with simple IP68 plastic things, and looks fairly smart (stays in place better than H07RN-F, your next type to try). They even do a cat-urine flavoured version for really desperate rat problems:
 
Last edited:
Cows are extremely sensitive to stray voltage. Had a milking parlour a few years ago where the bonding between the metal the cows stand on and the metal where they place their necks to feed had gone AWOL.
There was a fault elsewhere on the farm putting a small voltage on the earth wire, and the cows made it abundantly clear they didn't appreciate this voltage across their bodies. They refused to be milked, lashing out with their hooves, and the place looked like an explosion in a sewage works.
As for rats, they will attack any cable that gets marginally in their way. Route all cables under joists and beams where they cross them, never over the top, and run cables low down on the side when they run along joists.
 

Reply to electrical installation farm in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
764

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top