I have a grundfos sololift 2 wc1 macerator that isn't working. It's about 3 years old. When the toilet flushes the bowl just fills up but the motor does not kick in. There is power going to the unit, The macerator motor/pump turns freely. I took the motor apart in the hope that there may be debris, but nothing preventative(Just hair wrapped around the spindle). The small trip switches are in the correct position. There is power coming from the large capacitor and from what i assume is the pressure switch

Any advice on getting it working would be most welcome.

Thank you













 

Attachments

  • 20220303_194758.mp4
    45.9 MB
It looks like you are expecting too much from a non contact voltage indicator. These things have their (limited) uses, but aren't really suitable for close in voltage detection.
Having said that, it looks like you are detecting 'power' everywhere, including where there shouldn't be any, so the first thing I'd do is check the supply neutral is present.
 
Here is it with meter readings. 230v all around except for what i think is the pressure sensor which is reading about 16. 230 from the big cap too.
Any help would be really appreciated
thanks in advance
 

Attachments

  • 20220304_215040[1].mp4
    76.6 MB
There should be no significant voltage between the neutral (blue) supply wire and the earth (green/yellow) wire.
There are four terminals on that connector block, and parallax makes it difficult to see which wire you are testing, but it very much looks like you have full mains voltage between earth and neutral.
Could also mean that the earth is sitting at full mains, but I doubt it, since you have not electrocuted yourself.
 
the four block are two ins and two outs(live-brown, neutral-blue and two outs- both.black). If I have full mains voltage between earth and neutral, where it shouldn't be, what would you reckon is the cause of this and how would one go about fixing it?

again, Thanks in Advance
 
First place I'd look is at the other end of the supply lead. Turn off the power at the fusebox before removing the faceplate of any fitting.
Was the wiring for this unit done by the plumber who fitted it?
 
yes it was.. I have checked behind the face plate all seems in order. i also stuck a continuity tester between the live and neutral(with the power off) but there is no short.

Here is a schematic if it helps
 

Attachments

  • 20220304_231107[1].jpg
    20220304_231107[1].jpg
    216 KB · Views: 54
One would not expect to find a short or the fuse would have blown, but a continuity tester will read continuity across the motor winding if there is a circuit through the unit.


If I have full mains voltage between earth and neutral, where it shouldn't be, what would you reckon is the cause of this

Assuming that the earth is connected and intact, and that the unit is energised with the float switch closed and supposed to be running, then any part of the neutral wire that reads more than a few volts to earth is 'floating' i.e. not connected to the supply neutral. The break is between that section and the supply.
 
One would not expect to find a short or the fuse would have blown, but a continuity tester will read continuity across the motor winding if there is a circuit through the unit.




Assuming that the earth is connected and intact, and that the unit is energised with the float switch closed and supposed to be running, then any part of the neutral wire that reads more than a few volts to earth is 'floating' i.e. not connected to the supply neutral. The break is between that section and the supply.
I checked for continuity by removing the two wires from the cap that go to the motor. I am getting continuity there
 

Attachments

  • 20220304_233415[1].jpg
    20220304_233415[1].jpg
    294.7 KB · Views: 48
  • 20220304_233407[1].jpg
    20220304_233407[1].jpg
    267 KB · Views: 50
Need a pic of the inside of what is at the other end of the supply lead.
It's very likely there's nothing wrong with the macerator at a
seems to be three sets of twin and earth wires(Brown blue and green) Going into the switch and then a fourth flex leading to the macerator.
 

Attachments

  • 20220304_233407[1].jpg
    20220304_233407[1].jpg
    267 KB · Views: 44
  • 20220304_233415[1].jpg
    20220304_233415[1].jpg
    294.7 KB · Views: 42
  • 20220304_233423[1].jpg
    20220304_233423[1].jpg
    317.5 KB · Views: 49
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Dublin Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
Ireland
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Electrical problem with Grundfos macerator
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22
Unsolved
--

Advert

Thread statistics

Created
jazzguitar,
Last reply from
jazzguitar,
Replies
22
Views
3,462

Advert

Back
Top