I have received an unsatisfactory EICR report (with 12 nos C2 and 1 F1 code) and not sure should I get it done again by somebody else to get second opinion.
Any advice (i.e. cost and genuine faults needs rectification) on that will be greatly appreciable.
Poor condition of wiring, greening of cables in C/U and multiple socket outlets. No earth bonding to gas and water present. No CPC to multiple lighting points. Neutral conductor for ring final circuit has no continuity of conductors.
16 Compatibility of protective devices, bases and other components; correct type and rating (No signs of unacceptable thermal damage, arcing or overheating) (411.3.2; 411.4; 411.5; 411.6; section 432.433) - C2
17 Meter tails - F1
19 Confirmation of earthing conductor size (542.3; 543.1.1) - C2
20 Condition and accessibility of main protective bonding conductor/connections (543.3.2; 544.1.2) - C2
23 Presence and adequacy of circuit protective conductors (433.3.1; Section 543) - C2
25 Concealed cables installed in prescribed zones (see Section D. Extent and limitations) (522.6.202) - C2
26 for all socket-outlets of rating 32 A or less, unless an exception is permitted (411.3.3) - C2
27 for cables concealed in walls at a depth of less than 50 mm (522.6.202; 522.6.203) - C2
28 for cables concealed in walls/partitions containing metal parts regardless of depth (522.6.203) - C2
29 Provision of fire barriers, sealing arrangements and protection against thermal effects (Section 527) - C2
30 Connections soundly made and under no undue strain (526.6) - C2
31 No basic insulation of a conductor visible outside enclosure (526.8) - C2
33 Presence of supplementary bonding conductors, unless not required by BS 7671:2018 (701.415.2) - C2
Read more:
EICR Report Advice - https://www.diynot.com/diy/threads/eicr-report-advice.581701/#ixzz7CxySIZ36