Electrical Saftey Council Periodic inspection of existing domestic and similar Q & A

P

piggyitm

I've just been reading the Q & A guide and found that Q14 states

Q14. Is it acceptable to calculate (R1+R2) values when carrying out Condition Reports (PIRs), using measured loop impedance values?


No. In any event, it is not essential to measure (R1 + R2) values for a Condition Report.


Are they suggesting that you can skip the R1+R2 for a periodic?
 
Re: Electrical Saftey Council Periodic inspection of existing domestic and similar Q

In some circumstances yes.
For instance R1 + R2 does not have to be recorded or measured on radial circuits even during initial verification, if R2 is measured and recorded, or with PIRs if Zs at the furthest point is measured and recorded.
 
Last edited by a moderator:
Re: Electrical Saftey Council Periodic inspection of existing domestic and similar Q

If you have access to a previous PIR or EIC which has both R1R2 readings and Zs....it is acceptable to skip the R1R2 test and measure the Zs. As long as your measured value of Zs is substantially the same as on the previous cert it is reasonable to assume the R1R2 will be as well.
If not,as above...you will have to measure and record either R1R2 or R2.
 
Re: Electrical Saftey Council Periodic inspection of existing domestic and similar Q

Don't think Ive ever come across a job where they've had any certs!!!
 
Re: Electrical Saftey Council Periodic inspection of existing domestic and similar Q

Jobs have certs? Never been to a job that has had previous certs.
 
Re: Electrical Saftey Council Periodic inspection of existing domestic and similar Q

its not all its cracked up to be in the 'gate we have to do r1+r2 AND Ze cos there's never any certs
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
piggyitm,
Last reply from
piggyitm,
Replies
6
Views
1,322

Advert

Back
Top