Re: electrical separation for more than 1 item
The Earth to the sockets (on the output side) should not make any difference, they are not required, and serve no real purpose as with the 'isolated supply' neither side is live or neutral wrt earth, still 230 between the two line conductors though.
Have a look at the other thread you started about this subject, here:
http://www.electriciansforums.net/e...electrical-separation-more-than-one-item.html
I posted some extra info. last night in Post #9
And some info. in post #6 , on that thread