iceman
electrical seperation selv circuits
test between live conductors of each selv circuit connected together and the live conductors of any adjacent higher voltage circuits connect together
votage applied 500v dc
minimum test value 1.0 Mohms
for a circuit tht has serge protection and cant be disconnected
is it test between line and neutrel conductors connected together and test between earth?
voltage applied 500v dc
minimum test value 1.0 Mohm:cool:
Test the same but voltage of test can be dropped from 500v to 250v BRB 612.3.2 page 158. Where anything on a circuit may give a false reading I always test live and neutral on one clip earth on the other. and yes 1meg
Hope that helps
Chris
Reply to electrical seperation? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...