View the thread, titled "Electric showers" which is posted in UK Electrical Forum on Electricians Forums.

What’s the chances that both are being used at the same time? And is there anything else off this supply, however small?
 
What’s the chances that both are being used at the same time? And is there anything else off this supply, however small?
It’s a 3 phase supply with 4 showers proposed. It’ll be for school trips etc so I’d say there was a decent chance they’d be used simultaneously. I can split other loads over the other 2 phases but the 2 showers on one phase concerns me.
 
Ah I see. So it’s just a single phase sub main. No chance of another phase for this?


I’ve got a similar issue with 4 showers across 3 phases at a gym… but customer also wants 2 sauna rooms and electric heating.
3 phase 200A supply into building, but limited to 80A per phase at the cutout. I’ve told the customer to get it updated.
 
No diversity allowed on instant water heaters, so the official answer is no, it won't be compliant if both showers can be used at the same time.
 

Reply to the thread, titled "Electric showers" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland

Thread Information

Title
Electric showers
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Sparkystu79,
Last reply from
newfutile,
Replies
5
Views
166

Advert

Back
Top