Do not worry, so long as you are aware of the requirements (and have paid) you will be fine.
You do not actually require the EGTBR but it is useful and really you ought to have it (make sure it is the latest version)
Have a look at these documents from Elecsa regarding the assessment, they may help.
http://www.elecsa.co.uk/Documents/P...to-Avoid-Common-Part-P-Assessment-Issues.aspx
http://www.elecsa.co.uk/Documents/Public-Documents/Contractors/Guide-to-Part-P_2013.aspx
If you know this lot about the building regulations then you should be OK on that side.
Building Regulations Parts Applicable to Electrical Work
Part A - Structure
Vertical chases < 1/3 of wall/leaf, Horizontal chases <1/6 of wall/leaf, Chases not damaging wall
Notches in joists between 0.07 to 0.25 of span <12.5% of thickness
Holes in joists between 0.25 to0.40 of span <25% of thickness, Holes to be >3 o.d. apart
Part B – Fire Safety
Positioning and requirements for smoke and heat alarms.
Penetration of fire compartments and the maintenance of the fire resistance rating.
Penetration of fire resistant barriers and maintenance of resistance rating.
Fire stopping of cable penetrations.
Prevention of the spread of fire.
Part C - Resistance to the spread of contaminants and moisture
Prevention of water / contaminants from entering through external cable penetrations.
Prevention of water entering other areas from wet rooms.
Part D cavity insulation
Not normally applicable
Part E – resistance to the passage of sound
Maintenance of the sound resistance properties of walls and ceilings when making penetrations through sound resistant barriers. Both between dwellings and within dwellings.
Part F – Means of ventilation
Requirements for minimum flow rates in kitchens (60/30l/s), utitilty rooms (30l/s), bathrooms (15l/s) and toilets (6l/s) for intermittent extract ventilation.
Ventilation of rooms without purge ventilation (windows/doors) (15min overrun, no natural light operated by light switch)
Cooker hood heights (450mm-750mm from hob)
Air flow through rooms
Applicability to new and existing dwellings.
Part G – sanitation hot water safety and water efficiency
Part H – Drainage and waste disposal
Part J – Combustion appliances and fuel storage systems
Part L1A – Conservation of Fuel and power in new dwellings
Mainly use of energy saving lighting 75%: >45lm/W (if >5W)
Also external lighting to be photocell + movement sensor controlled or energy efficient
Part L1B – Conservation of Fuel and power in existing dwellings
Mainly use of energy saving lighting in area worked on 75%: >45lm/W (if >5W)
PartL2A and PartL2B Conservation of Fuel and power in new / existing non dwellings
Not applicable to Part P
Part M - Access to and use of buildings
Generally just height of switches and sockets >450mm<1200mm
Consumer units accessible
Accessibility of switches, outlets and controls –Height, labelling, consistent location, visual ease and lack of obstruction. Some exceptions (floor sockets).
Part N – Glazing safety
Not applicable
Part P – Electrical safety
Design, install, inspect and test in accordance with BS7671. Work in accordance with H&S requirements. Notify building control for certain higher risk work, or be member of a self certification scheme.
Definitions of notifiable work(England) : New circuits, alteration of circuits in zones of bathroom or in rooms containing saunas, swimming pools, new consumer units.