I am having some problems with an Elat variable speed 3 phase fan controller which I have installed in a restaurant.
The speed controller (149-TC33) is rated at max peak current 3A and the fan that is being controlled runs at 2.9 amp according to the manual.
Fan is also Elta (SMC560/4-5-3) and this setup was recommended by Elta. The problem is that the speed controller transformer has burned out after a few hours. I was very apprehensive at installing the 3A rated controller given that the running current of fan is so close at 2.9. I did clamp meter all three phases which were sitting at around 2.7 - 2.8.
Should this fan be controlled by the higher rated (5A) controller or should this setup have been ok?
According to Elta's website spec sheets the transformer speed controller was correctly specified. You did right to clamp all three phases and the run currents sound good. I'm not personally familiar with the specific fan or speed control so I have a couple of questions; did the fan have 2 thermistor wires in the motor terminal box? Did you connect them? Also what overload/missing phase protection does the circuit have?
When you say the speed controller burned out can you be more specific about the damage? Maybe post a photo or two if there was anything that could be seen as damaged.
From what you've said I don't see any reason it would have gone toes-up. Most common causes of failure would include incompatible speed controller, incorrect wiring, phase failure, poor terminations and reverse rotation. From your test results and statements none of these stand out as particularly likely as nearly all of them would show up as high run currents.
Just clamped the amperage again. When running on speed 5 (full) the run current is 3a but when I adjust to speed 3 the current settles about 5a is this normal? And if not what would cause this?
Reply to Elta fan controller problems in the UK Electrical Forum area at ElectriciansForums.net
You are quite welcome my friend and good luck. I wasn’t trying to insult your intelligence and sorry if it seemed that way. Have a great day
Thank you for the update. It's always nice to know that a problem has been solved, or at least understood! Unfortunately not all those seeking...