I am wiring a premises that contains a Main Distribution Board and two Sub Distribution Board (SDB).
I have wired a central test unit (CTU) in each sub board for the relevant emergency lighting in the area that the SDB is feeding, however the architect wants just one central test unit in the Main Distribution Board to test all of the emergency lighting.
Is it acceptable to have a CTU in each SDB?
Each circuit, controlled by a mcb/rcbo must be identified per area, and tested as such. So either an addressable EM controller, separate keyswitch area contro,l or a central contactor controlling all EM circuits from a central keyswitch identified as such.
I have wired a central test unit (CTU) in each sub board for the relevant emergency lighting in the area that the SDB is feeding, however the architect wants just one central test unit in the Main Distribution Board to test all of the emergency lighting.
Is it acceptable to have a CTU in each SDB?
Each circuit, controlled by a mcb/rcbo must be identified per area, and tested as such. So either an addressable EM controller, separate keyswitch area contro,l or a central contactor controlling all EM circuits from a central keyswitch identified as such.