Hi
I have recently carried out an electrical installation in a small office unit that will be occupied by the public and around 5-10 office staff its a showroom
I have installed non maintained emergency bulkheads within the property and exiting signs on the exit positions
The problem I have is that a contractor has been in to carry out extra installation works within the office
The contractor has told the client that the emergency lighting should be on its own dedicated circuit form the distribution board
The way I have wired the emergency lights is that I have taken a 1.5mm twin and earth from the distribution board to a a switch then from the switch I have wired the general lights as a switch feed from the switch then the emergency bulkheads have been feed using a 3 core and earth via a double pole key switch from the main switch position
I would like a quote from BS5266 if possible, I do have a copy but I am unable to gain access to it at the time being
Thanks
I have recently carried out an electrical installation in a small office unit that will be occupied by the public and around 5-10 office staff its a showroom
I have installed non maintained emergency bulkheads within the property and exiting signs on the exit positions
The problem I have is that a contractor has been in to carry out extra installation works within the office
The contractor has told the client that the emergency lighting should be on its own dedicated circuit form the distribution board
The way I have wired the emergency lights is that I have taken a 1.5mm twin and earth from the distribution board to a a switch then from the switch I have wired the general lights as a switch feed from the switch then the emergency bulkheads have been feed using a 3 core and earth via a double pole key switch from the main switch position
I would like a quote from BS5266 if possible, I do have a copy but I am unable to gain access to it at the time being
Thanks