I think you'd struggle on price in the commercial sector as well as twin and earth is very versatile and used everywhere for fixed wiring These days , unless specified differently by the client it's here to stay.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Emergency lighting wiring in the Electricians Chat - Off Topic Chat area at ElectriciansForums.net
Why the ban on T&E?LOL well the usual way is to use singles in containment. Then these can be of the correct colour throughout their length, as preferred by BS7671.
It's no secret that T&E type cables (and three-core and Earth for that matter) are designed for domestic installation. Their use in non-domestic installations is certainly not something to celebrate!
Incidentally, as much as I despise T&E, I now have to stock two different types of T&E as of this day last week. The traditional T&E was banned in the south of Ireland a week ago (although there were already certain differences such as 16mm^2 T&E had a 10mm^2 cpc instead of a 6mm^2 one).
As opposed to banning T&E, IS 201 has changed the requirements for it. This has been in the pipeline for a number of years, with the Amendment to the Wiring Rules being implemented from last Tuesday. What this means is that all sizes of T&E now have an insulated cpc instead of a bare cpc. Also the cpc is of the same cross-sectional area as the live conductors. The use of the old type T&E from the 5th September 2017 has been prohibited.Why the ban on T&E?
As opposed to banning T&E, IS 201 has changed the requirements for it. This has been in the pipeline for a number of years, with the Amendment to the Wiring Rules being implemented from last Tuesday. What this means is that all sizes of T&E now have an insulated cpc instead of a bare cpc. Also the cpc is of the same cross-sectional area as the live conductors. The use of the old type T&E from the 5th September 2017 has been prohibited.
I despise T&E because it is cheap domestic cable which is widely misused. .
Yes you can carry out an adiabatic calculation with singles instead of selecting from a table (much like BS7671) - however, it isn't a common approach. I presume that the reason for the full size cpc is largely due to harmonisation.Any idea why these requirements were brought in? Have there been any incidents which have occurred as a result of uninsulated CPC's or some technical reason for the change?
Do the regulations generally require cpcs to be of the same CSA as the line conductor in all wiring, or is it unique to T&E? Are you permitted to calculate the require s size of CPC if using singles for example?
Reply to Emergency lighting wiring in the Electricians Chat - Off Topic Chat area at ElectriciansForums.net