Besides running men and emergency exit signs over exits staircases etc got me thinking is there a set ratio of how many emergency lighting would be installed in offices classrooms etc
 
Again off the top of my head 8w tube fittings would need to be spaced 11-12m apart to achieve 1 lux on edge or overlapping areas. Led i would think would easiler give you more spacing

No where near 11-12m!, it normally just under 2m from a door or wall and 6m between fittings to achieve 1lux

you may be referring to the old regs which was only 0.2 lux on escape routes, this is now non-compliant

you also need open area lighting in all rooms over 60m2 and with emergency escape routes running through it, this needs to be lit to 0.5 lux min

download the ICEL emg lighting spacing table data off google, it has the spacing data for most standard types of fittings, you can also use this as your evidence for photometric data compliance within your emg cert, which is invalid without
 
No where near 11-12m!, it normally just under 2m from a door or wall and 6m between fittings to achieve 1lux

you may be referring to the old regs which was only 0.2 lux on escape routes, this is now non-compliant

you also need open area lighting in all rooms over 60m2 and with emergency escape routes running through it, this needs to be lit to 0.5 lux min

download the ICEL emg lighting spacing table data off google, it has the spacing data for most standard types of fittings, you can also use this as your evidence for photometric data compliance within your emg cert, which is invalid without

Yes 6m per side so spacing from on em light to the other 12m between the two.....if a em light cant produce 1 lux in all positions over a 10mx10m I would look at new lighting
 
Amazed no one has advised you to talk to a professional regarding this. When designing emergency lighting systems you need to know your stuff, we can all advise you all day long, but IMO and IME getting someone else to take the design responsibility is the best way I think, We all know about 2 lights lighting each escape route and signs showing the way out etc, but I like someone else to take the pressure in this easily installed but difficult designed area, an electrical engineer via a consultancy would be my preffered option
 
Yes 6m per side so spacing from on em light to the other 12m between the two.....if a em light cant produce 1 lux in all positions over a 10mx10m I would look at new lighting


No its 6m between fittings, the spacings take account of the drop in the lumen output due to age/dust on lense etc a worst case condition if you like

this is why its not good enough to use a lux meter on new fittings to check lux levels, as the lamps are brand new and clean, and will easily acheive 1lux
 
No its 6m between fittings, the spacings take account of the drop in the lumen output due to age/dust on lense etc a worst case condition if you like

this is why its not good enough to use a lux meter on new fittings to check lux levels, as the lamps are brand new and clean, and will easily acheive 1lux
Would hope on a new fitting I would be see a least 5-10 lux......that whats I would be be designing and cading positions on the drawings to achieve this.
 

Reply to Emergency lighting in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
The company Liteplan do replacement modules: Liteplan – The UK's largest emergency lighting component supplier. - https://www.liteplan.com/ This...
Replies
5
Views
588
  • Question
Or a combined fitting in each row.
Replies
19
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top