Help please - has anything changed on EPc requirements on landlords supply? Does an epc/exemption need doing for the communal areas or not as I am getting conflicting information and not registered one like this for ages!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss EPC Landlords supply! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Depends on the detail of the metering.
If the landlord has the only MPAN meter and uses his own meters to sub-meter to tenants then the whole building would be classed as the 'site' under FiT terms and an EPC would be needed.
If each individual tenant has their own MPAN meter then it could be argued that the 'site' is only the landlord's part of the building and if that does not have any heating then it could be exempt from the EPC requirement. If there is heating in the communal area then it is going to need an EPC.