The regs may not be the law, however you would have to prove that any design that was installed without using BS7671 regs was safe. Fine if you are a qualified designer but very hard I would have thought for a lot of us.
Because BS7671 is non statutory then you cannot be prosecuted for not complying with the regs. However you could be prosecuted under the EAWR which is statutory law. In the abscence of comprehensive design criteria the only defence for you to prove a safe installation, is to follow BS7671, and prove you have followed it.
As a warning, a mate of mine (NIC approved contractor) was called out to a job, by a plumber, about a month ago. It was an older property with suspect wiring (old rubber IIRC).
The plumber was originally called out because the owner had boiling water coming out of the mains cold tap in the kitchen. Being fairly clued up the plumber put a clamp meter around the mains pipe to the tap. There was 40 AMPS!! being put through the mains pipe from the dodgy wiring. It was heating the water to boiling point!!
Guess what? being an older property there was no Equipotential Bonding.Thank god the plumber knew what he was doing and didn't touch the pipework.
Brought home the importance of ME bonding to me!!
Am not saying dont earth the pipework all a was saying is that if your readings meat the 17th edition regs !! then surely the 6mm should be fine!!!a think by the time we get to the 18th edition we will be running 16mm earths and more earths to individual circuits!!! a think they go a bit o.t.t at times personally!!!!