Hi all. Will have to forgive me for enquiring about basic question but would rather be sure of all considerations than not. Went to view property for potential EV install yesterday. On viewing intake of property I realised supply had been converted from PME to a TT supply. I'm unsure why they may of done this? The property does have solar power, could this possibly have been a consideration why they converted this?
The whole install is protected upstream with 100ma RCD then to household dual RCD board. I took a quick ZS reading at intake and was 100ohms which is acceptable to me. My plan for EV as will be situated conveniently next to outdoor intake cupboard will be to split supply from 100 amp connector and from here take new supply tails to new dedicated EV A type RCD consumer unit and take my main earth from main earth block. In this situation there will be no 100ma upfront RCD. As not great deal of experience regarding TT installs just wondered if anyone thinks I'm missing any considerations here?
Thanks
The whole install is protected upstream with 100ma RCD then to household dual RCD board. I took a quick ZS reading at intake and was 100ohms which is acceptable to me. My plan for EV as will be situated conveniently next to outdoor intake cupboard will be to split supply from 100 amp connector and from here take new supply tails to new dedicated EV A type RCD consumer unit and take my main earth from main earth block. In this situation there will be no 100ma upfront RCD. As not great deal of experience regarding TT installs just wondered if anyone thinks I'm missing any considerations here?