I'm looking at installing a 7kW EV charger on an outbuilding with the following characteristics:
Having done the cable calculations for the 7kW charger, it looks like at least 10mm will be required. Am I correct in therefore assuming that I will have to run a completely separate supply cable to the outbuildings or replace the current one?
I just want to make sure that the current installation is not appropriate for the charger before digging a very large trench!
Any guidance would be appreciated. Thanks.
- EV charger will be 60 metres from the main fuse where there is an initial small consumer unit in the meter cupboard.
- Currently there are 2 extra small consumer units for each outbuilding, each with an RCD as a main switch.
- EV charger will be at the furthest point beyond the third CU.
- The SWA to the first outbuilding is 6mm.
- The SWA between the buildings is also 6mm.
- There is a solar array on the outbuildings.
Having done the cable calculations for the 7kW charger, it looks like at least 10mm will be required. Am I correct in therefore assuming that I will have to run a completely separate supply cable to the outbuildings or replace the current one?
I just want to make sure that the current installation is not appropriate for the charger before digging a very large trench!
Any guidance would be appreciated. Thanks.