Hi
Doncaster EV ultra cable:
Does anyone know what the current capacity of these cables is given particular reference methods?
The spec sheet just says 'Max current' 45amps (for the 4mm) but it doesn't state the reference method.
The manufacturer does have a very handy cable calculator tool but I'm not sure which category of cable the EV ultra falls into.
Many thanks
It's 90 degree thermosetting multicore so table 4E2A applies (subject to 90 degree operation being possible)
If its the armoured version then 4E4A.
Obviously if you're limited to a conductor operating temperature of 70C then you'd need to use the appropriate 70C tables.
Reply to EV ultra cable, current carrying capacity in the UK Electrical Forum area at ElectriciansForums.net
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...