Hi all, first post on the forum and I hope you's can help me with a few questions I have.
I have been asked to test a caravan site with the following details
pme supply (with no individual spikes at hook up points)
main 400a mccb with bolt on adjustable rcd(turned in the off position)i.
I have the previous paperwork from 3 years ago but it states that the supply is tns but on the end box it says pme.
Many of the submain circuits exceed the max zs reading stated by bs7671.
My main questions are
1. Is the main mccb with bolt on rcd to provide the correct disconnection times on the circuits with high zs readings
2. Is the only way to fix the pme side of it to drive spikes at each individual hook 1up point.
If any of you's could shed a bit of light on this I would be grateful , thanks Dean