Hello, first time poster, long time viewer. Testing a school which on the socket circuits have BS 3871 type 3 breakers with a 30ma RCD attached. Some of the socket circuits exceed the 0.72 ohms max zs for the breaker. Should I be using the max zs as 1667ohms? I seem to remember that if max zs cannot be achieved then an RCD could be used, or have I got that wrong? Yes I am an electrician.
 
One has to ask, why are these socket circuits being protected by a Type 3 MCB's??

I'm the wrong person to ask, as far as making use of 30mA RCD to circumvent a fixable circuit Zs failure. I'm definitely in the ''only as a last resort'' camp!! ..lol!!
 
I Don't like the Idea of RCD's in use for high Zs readings ,and RCD is there for additional protection , there is way to much reliance on RCD's, if the circuit Zs is within that laid out by the regs then the disconnection time should be met ,without the use of the RCD, what im really getting at is if the RCD fails and the Zs is high then the circuit my well not disconnect but within the max Zs then the required time should be met , see what I mean
 
Without telling us the Zs you recorded its hard to give an accurate reply. The RCD could have been selected due to the environment the circuits are in, for example chemistry lab with wet areas and lots of portable equipment with long trailing leads.
I personally would consider installing a type 2 or 'B' type as this is what is recommend for socket circuits unless demand requires otherwise for example heavy inductive loads etc creating high inrush currents.
Using RCDs to 'beat' the system when high Zs are found is all to common, especially without proper further investigation to determine the causes of the original high Zs.
Find out length of run etc, see if you can select 'B' type MCB.
 
^^^^^^
It's weird he can remember all his regs details, standards codes of practice etc lads but ask the guy to remember the
T-bags when it's his turn and he fails to deliver.
Just a reminder any chance of a brew tomorrow Mr Trim
 
411.4.9

Whilst some don't like it, its valid to use an RCD if the Zs for the overcurrent device is too high. Although you have to make sure the impedance for a L-N fault will trip the overcurrent protection!

And quite a few people I've noticed don't seem to understand that RCD is 'earth fault' and nothing to do with overload or short circuit !
 

[ElectriciansForums.net] Exceeding Max Zs
Originally Posted by yellowvanman [ElectriciansForums.net] Exceeding Max Zs
411.4.9

Whilst some don't like it, its valid to use an RCD if the Zs for the overcurrent device is too high. Although you have to make sure the impedance for a L-N fault will trip the overcurrent protection!

Wow!! These sort of comments really makes one wonder, what's going on out there??
 
Points taken, thank you for the replies. The Zs recorded were above the max zs ,1.01 being the greatest reading of one of the circuits. I have flagged it in the report and will try and source the B type breakers. I was just curious as to whether the additional RCD protection would be acceptable in this case. My gut instinct was that it was wrong, but in a TT system you rely on the RCD where the disconnection times cannot be met. Thanks again.
 

Reply to Exceeding Max Zs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
920
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
705

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top