Excessive earth fault loop impedance | on ElectriciansForums

Discuss Excessive earth fault loop impedance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Feb 18, 2014
Messages
31
Reaction score
1
Location
Wallington
I work for a hotel chain and recently we’ve had our 5 yearly test they have 8 circuits from our LV panel with excessive loop impedance readings !! So apart from either introducing an rcd or dropping mcb ratings or type is there any other way of achieving satisfactory readings ??
Also if I have a fuseboard fed from another fuseboard ie a distribution circuit when doing a certificate is the (ze) on the furthest board recorded as a zs I think it’s called a zdb I’m just trying to understand there report as it doesn’t state anything just high loops
Can someone advice me please

[ElectriciansForums.net] Excessive earth fault loop impedance
 
it sounds like maybe the Ze is excessive or a fault with main earthing. need far more info to make an accurate diagnosis.
I’m going to the hotel tomorrow to have a look will provide more info then but if it is the ze wouldn’t all the circuits have a high reading ?
Also regarding zdb is the ze from another dB recorded as a zs reading ?
Many thanks for your reply
 
I’m going to the hotel tomorrow to have a look will provide more info then but if it is the ze wouldn’t all the circuits have a high reading ?
Also regarding zdb is the ze from another dB recorded as a zs reading ?
Many thanks for your reply
yes. your Ze is the EFLI at source of installation.all readings downstream ( after main earth) are Zs. ( sometimes referee to as Zdb at dis. boards. ) these Zs readings are taken with bonding connected, as opposed to the Ze where bonding is not.
 
Presuming that the LV panel contains mccb’s then It could be that either the maximum zs that the inspector has allowed for the device is incorrect and it actually complies(manufacturer’s data is required) or that the original install , incorrect maximum zs values for the ocpd was incorrectly assumed to comply when in fact it never did.

Or as others have said the Ze is on the high side.
Some results/values of the excessive zs values might help
 
Last edited:
Another thought, how close is the main DB to the supply transformer and has the tester used a MF meter that is suitable with a high current test facility?
Standard domestic type MF meters can give incorrect Zs readings if close to the supply transformer.
 
Do you have a previous or better still initial report/certificate? as for your question other than what you posted to overcome this would be the increase of conductor size/additional earth.
 
Hi sorry for delay I’ve been to the job and they are protected by Berlin gerun BS100N Mccb I have 3 phase 100a and single phase 63a and 32a they are saying max zs is 0.10 for these can anyone confirm or tell me what the max zs is for these many thanks

[ElectriciansForums.net] Excessive earth fault loop impedance

[ElectriciansForums.net] Excessive earth fault loop impedance

[ElectriciansForums.net] Excessive earth fault loop impedance

[ElectriciansForums.net] Excessive earth fault loop impedance

[ElectriciansForums.net] Excessive earth fault loop impedance
 
Another thought, how close is the main DB to the supply transformer and has the tester used a MF meter that is suitable with a high current test facility?
Standard domestic type MF meters can give incorrect Zs readings if close to the supply transformer.
Andy, I found this post of yours from four years ago. We (I am the QS) are having some issues with larger (400A -1250A) MCCBs/ACBs having excessive Ze readings. What do you mean when you say MF meter? Is this like a Megger 1711 or something like? [email protected]
 

Reply to Excessive earth fault loop impedance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
2K
Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...
Replies
6
Views
875

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top