Dear all


I have been asked to quote for some work at a property and am concerned at the maximum demand already present without me actually adding to it.


I would therefore welcome any thoughts on just how much diversity I can apply.


The consumer unit currently has ten circuits as follows:-


2 NÂş lighting circuits with 6 A MCBs
1 NÂş Immersion heater (assumed to be 3kw) 16 A MCB
3 NÂş Socket outlet circuits 32A MCB
1 NÂş 9kw shower 40 A MCB
1 NÂş Oven Circuit + integral Socket Outlet 32A MCB
1 NÂş Hot Tub, rating plate is 25A but on 20A MCB
1 NÂş Wise Box wireless remote control distribution box, rated at 40A but on a 20A MCB


The incomer is a standard 100A and the consumer unit is a Contactum unit also rated at 100A


The wise box currently has 1 NÂş 2.1kW heater, 1 NÂş 1.5kW heater and a total of 460W of lighting.


The job I've been asked to quote for includes adding another 2.1 kW heater to the wisebox including replacing the feed cable to suit – this would bring the maximum demand of the wisebox to 26 A so obviously a new MCB is also required.


The cooker is being replaced by a new double oven which according to the client needs a 20A feed (probably actually a 4.4kW)


We are also adding a new ceramic hob which according to the client needs a 30A feed. This obviously means replacing the consumer unit with a larger one as we have no spare ways.


My problem is that whilst calculating diversity for the new and existing kit, before I even get to the socket outlet and lighting circuits I am at 134 Amps.


Without the additions I believe we stand at over 100 Amps and again this is without the three socket outlet circuits and the two lighting circuits.


I appreciate the OSG states “The information and values are....only for guidance” and that “the values given in table 1B...may be increased or decreased” but the size of the excess here seems too big for me to claim “I know better than the book”.


I did raise my concerns the issue of maximum demand when I visited – I'm on the verge of telling the customer I can't do it.


Any advice would be greatly welcomed.


Cheers


Ken
 
i think you would be hard pushed to exceed 100A. ensure that your tails are 25mm and the earthing and bonding are satisfactory. get the job done. then if the customer has an issue with excess load, it's time for him to dig deep and contact the DNO.
 
"1 NÂş Wise Box wireless remote control distribution box, rated at 40A but on a 20A MCB"

As Telectrix states you will be hard pushed to go beyond 100A unless you are going to hold regular Arc welding parties at the bottom of the garden.

As I remember it, the Wisebox RF controller has 4 outputs rated at 10A fused per output for the 866MHz and the older one 434MHz was 16A unfused outputs. I assume that you are using 1* 2.1kW heater per output? I've never attempted to run 4 *10A loads through them as the small output relays do not look as though they could cope with switching that amount of current.
 
all the methods of determining max. load are at best a guesstimate, and err on the side of caution. just don't let them talk you into fitting a couple of 10.5kW showers.
 
Dear All

Thanks for your very prompt replies, I totally agree with all of them however it does make applying the OSG's diversity table seem pointless.

In reply to ackbarthestar, each heater will be on a seperate circuit with the lighting on the fourth -I would expect all of these to be on at the same time along with the hot tub (which is never turned off but obviously has a thermostat so is not always drawing 20/25A).

What value would you guys recomend I put in my Certificate for the MD? I would propose 100A but that looks as if I haven't worked anything out.

Cheers

Ken
 
I did raise my concerns the issue of maximum demand when I visited – I'm on the verge of telling the customer I can't do it.

Why not raise those concerns with the customer,outlining the issue and explain that calculating that maximum demand is not an exact science

Highlight the worst case scenario and let them make an informed decision

Turning down the job because of your doubts about supply capability, is not, in my opinion, your best decision,that decision does not need to be taken by yourself
 
problem is if he frightens the customer off having the work done, knowing the sort of cost involved getting DNO to upgrade a supply. i would think that if the 100A was ever exceeded, it would be of too short a duration to take out the supply fuse.
 
Yes I have to agree with you tel,his proposed loading just looking at his circuits is to an extent bog standard for a Domestic supply

I agree also with frightening them with the supply upgrade cost,but its better than just turning away


On a lighter note,I am supposed to be filling out quite a few certificates, but I have a problem :sad_smile:

I find it so boring that in the last half hour its been
Test certificates 0 minutes
Forum watching 25 minutes
Making tea and a smoke 5 minutes

At least the Mrs thinks I am knuckling down to the task :tounge_smile:
 
Last edited:
i'd just crack on and get the job done. switch on as much as i possibly could , then clamp the incomer tail. if it looked as if it could be excessive, i'd then advise the client accordingly. ( fdull steam ahead and damn the torpedoes. even if it's durham at the periscope).

edit:eek:r should i say , especially if it's durham at the periscope.
 
Last edited:
"1 NÂş Wise Box wireless remote control distribution box, rated at 40A but on a 20A MCB"

As Telectrix states you will be hard pushed to go beyond 100A unless you are going to hold regular Arc welding parties at the bottom of the garden.

As I remember it, the Wisebox RF controller has 4 outputs rated at 10A fused per output for the 866MHz and the older one 434MHz was 16A unfused outputs. I assume that you are using 1* 2.1kW heater per output? I've never attempted to run 4 *10A loads through them as the small output relays do not look as though they could cope with switching that amount of current.

I seriously thought i was the only one who had Arc welding parties....im so relieved. I just love all the slags........
 

Reply to Excessive Maximum Demand and Applying Diversity in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I...
Replies
13
Views
892
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
602

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top