Testing 2 exhibtion trailers with the same setup. Power is provided by a generator with a main switch which runs to a consumer unit about 1 metre away. The consumer unit main switch is an RCD, the CU then houses 5 MCB's. Now theres no OPD placed between the generator and the consumer unit but is this a problem?.

4 16A MCB's and 1 10A MCB the generator is easily capable of this load. The consumer unit is fed with 25mm tails. Now BS7671 says overload protection may be placed along the run of a cable within 3 metres which it is. But the only overload protection provided are the MCB's.

Do you see a problem here? What code?. The whole installation is abit of a funny setup, Ive been scratching my head quite a few times with different problems thinking is this acceptable, and just left with this one.

Thanks.
 

Reply to Exhibition Trailer Generator in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I...
Replies
13
Views
984

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top