OP
Netzero1967
DIY
Does that mean i do not need an additional earthing rod? I paid good money for the EICR report.Just very quickly looked and stunned
Figures are nonsense, data entered is wrong everywhere I look. He has NO understanding of what he is doing. None.
From the intake information , protective devices details and on and on .
TT system suggests the distributor will not provide the means of earthing for the consumer. By way of but one example, this can be because the distributor cannot guarantee the earth connection. This is common where the intake supply is by way of LV overhead supply which perhaps you have.
As such there is no Distributors Earthing arrangment to code against!