Customer has a large metal caravan with three phase supply feeding 3 metal Consumer units with split load RCD outlets contained within - all circuits originate form a RCD. The Boards are then fed from a TP isolate a few feet away, the earth is disconnected on eth SWA and a rod installed near by. ZS ifs pretty good around 30ohms or so.

There are is no RCD in line with the supply to the boards. These are MK Sentry CUs, and the internal wiring is only single insulated and as i read the OSG p21, there should be an RCD in series with the supply offering protection from internal shorts within the CU - a TT system.

I just checked and it seem that MK do not offer an S type RCD.

They do offer a 100mA RCD. As all final circuits are covered with 30mA RCDs, i was planning to use the 100mA RCD and replace the isolator module in each of these boards with one, thus covering the internal Bus Bar and cabling.

Why is it 100mA and not less mA? I tried to find in the regs but could not see.
Would i still get issues with nuisance tripping seeing as it is not timed?

Do i just cut my losses and install a separate 100mA timed RCD?

Thanks

John
 
Last edited:
So not needed at all if if final circuits 30mA protected and meet the installation methods mentioned .. learning day
Unfortunately whilst i have RCDs and RCBOs in these boards, bus bars are not insulated and interconnecting cables are standard MK single insulation, so i will need to fit an RCD in series with the supply.
 

Reply to Existing split load 17th Install RCD question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K
Ok I’ll try this when I’m down
Replies
4
Views
378

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top