Hi All,

I am not a qualified electrician - please be gentle!

I had renovation done to my house last October which included a complete refitted kitchen. The new kitchen included a new Neff double oven in which has been working like a charm since last it was installed (including both ovens being on at the same time!).

Suddenly, yesterday the double oven has decided to stop working, checked the distribution board and nothing has tripped. I have tried getting in touch with the electricians that did the installation, but has failed to get back in touch. Therefore, decided to investigate the matter further. I put my multi-meter over the live and neutral terminals on the oven and it read 150V AC, I have checked the outgoing voltage at the MCB which read 240V AC. I thought I may either have:

1. a bad switch
2. a bad MCB
3. a bad connection
4. may be an earth leak

I have tried changing the switch and the MCB, no change to the volt reading [whilst disconnected from the oven]. I have tried tightening the terminals within the distribution board in case of loose connections, no such joy!

Other observations, I noticed that the cable exiting the oven is BLUE and BROWN whereas the cable leaving the distribution board is RED and BLACK. I cannot find the join for this cable as I fear it may be tucked behind the newly plastered walls and ceilings!

Any assistance or information on how to rectify the above volt drop without punching holes about the house would be much appreciated.

Many thanks,
Brian
 
Did the "Electrician" leave you with any certification, did the company belong to any of the Schemes NICEIC,NAPIT STROMA? it could be that the "Electrician" was in fact Kev the Kitchen fitter, ergo not an Electrician. I could be that he connected your oven / cooker to a cable that is far to small for the intended use you require at present, I'm not saying this is the case, as I'm only going on the information you have given.

If the company doing the renovations were allied to any of the schemes, your first port of call would be to whichever scheme they belonged to, if not, then call a local registered Electrical Contractor and ask them for an assessment of your problem. Good luck with your investigations I hope it turns out to be a minor problem easily rectified.
 
Is it on a fused switch which should be in the wall somewhere? If so check all terminations are good and check fuse.

The oven itself may have a fuse.

sounds like power to the cooker is good

always make sure you cut the supply at the cu via the mcb or better switch the main power switch off if you don't have the correct tools to make sure supply is in isolated.
 
Its best you get a qualified sparky in to check it out for you. The oven worked fine for a short period, then just suddenly stopped working properly and you are certain its not the oven?

If its definitely not the oven then there must be a fault that's appeared on the circuit supplying it. If all else is ok, to get such a dramatic voltage drop can only indicate a fault of some kind.

No offense, but a decent spark will be able to verify your voltage drop, do other fault finding tests and then proceed to try and find the culprit of the problem. But be prepared as it may indeed require some disruption. Unfortunately this may mean searching for and "digging" out any hidden joints.
 
Last edited:
Is it on a fused switch which should be in the wall somewhere? If so check all terminations are good and check fuse.

The oven itself may have a fuse.

sounds like power to the cooker is good

always make sure you cut the supply at the cu via the mcb or better switch the main power switch off if you don't have the correct tools to make sure supply is in isolated.
Not at 150v it's not.
 
A usual case (though this may not be your case) for an oven or cooker is a loose connection overheating and causing a partial or complete disconnection.
The location of this overheated connection is normally obvious as the accessory also starts to melt or discolour.
The normal run of cable would be from MCB to cooker isolator switch (on kitchen wall or in kitchen cupboard) to cooker outlet point (behind cooker) to flex or twin and earth to cooker.
It is possible that your cooker is supplied form a socket circuit (which it should not be) if there was only a single oven there before.
The different colours of cables could be because the cooker circuit from MCB to switch was not changed but the part after the cooker isolator was changed.
Correct identification of the circuit involved and safe isolation of the circuit are critical to safety.
It is generally best to test the resistances of a circuit whilst it is totally disconnected from the power supply and not to attempt to monitor voltages on a live circuit. Professional assistance should help in this regard.
A logical approach is also useful and just changing items, whilst it may cure a problem, means the reason for the problem is not known and can cause a repetition later.
Being alive is more important than a non working oven, so ensure safety at all times.
 
Be very careful, from what you say it could be an open circuit neutral in which case the neutral wire will be at a high voltage with respect to earth so in laymans terms you could get a shock from the neutral wire as easily as you could get a shock from the live.
 
Is it on a fused switch which should be in the wall somewhere? If so check all terminations are good and check fuse.

The oven itself may have a fuse.

sounds like power to the cooker is good

always make sure you cut the supply at the cu via the mcb or better switch the main power switch off if you don't have the correct tools to make sure supply is in isolated.

The power to the oven is not good, it is currently reading 150V AC between the live and neutral terminals. The MCB [granted is an older type Crabtree SB6000 type 1] outgoing terminals is still reading 240V AC between the live and neutral terminals.


You need to locate a local competent spark.

Where are you based?

Glasgow.

How on, you've changed an mcb?

if your not competently experienced I wouldn't suggest taking on work like that. It can kill you

I would say that I am academically experienced and had previous experience in control panel / LV & MV switchgear panel building for various industries, now an instrumentation commissioning engineer whereas I rarely touch anything over 24V DC!

Its best you get a qualified sparky in to check it out for you. The oven worked fine for a short period, then just suddenly stopped working properly and you are certain its not the oven?

If its definitely not the oven then there must be a fault that's appeared on the circuit supplying it. If all else is ok, to get such a dramatic voltage drop can only indicate a fault of some kind.

No offense, but a decent spark will be able to verify your voltage drop, do other fault finding tests and then proceed to try and find the culprit of the problem. But be prepared as it may indeed require some disruption. Unfortunately this may mean searching for and "digging" out any hidden joints.

Certainly not the oven no, I have disconnected the oven from the switch [after isolating the mains supply and proving dead!] and tested between the live and neutral terminals and it read 150V AC. I am now starting to feared the worse that I may need to start bashing holes about the house looking for phantom cable joint(s).

A usual case (though this may not be your case) for an oven or cooker is a loose connection overheating and causing a partial or complete disconnection.
The location of this overheated connection is normally obvious as the accessory also starts to melt or discolour.
The normal run of cable would be from MCB to cooker isolator switch (on kitchen wall or in kitchen cupboard) to cooker outlet point (behind cooker) to flex or twin and earth to cooker.
It is possible that your cooker is supplied form a socket circuit (which it should not be) if there was only a single oven there before.
The different colours of cables could be because the cooker circuit from MCB to switch was not changed but the part after the cooker isolator was changed.
Correct identification of the circuit involved and safe isolation of the circuit are critical to safety.
It is generally best to test the resistances of a circuit whilst it is totally disconnected from the power supply and not to attempt to monitor voltages on a live circuit. Professional assistance should help in this regard.
A logical approach is also useful and just changing items, whilst it may cure a problem, means the reason for the problem is not known and can cause a repetition later.
Being alive is more important than a non working oven, so ensure safety at all times.

Very true, nobody has received an electric shock from the oven - I have in the meantime isolated the MCB until the problem has been rectified. Curious though, if there was to be a fault in the circuit, wouldn't it have tripped the MCB or the RCB?

Be very careful, from what you say it could be an open circuit neutral in which case the neutral wire will be at a high voltage with respect to earth so in laymans terms you could get a shock from the neutral wire as easily as you could get a shock from the live.

I recall an electrical engineer telling me the exact same thing, that you could potentially receive a bigger belt from the neutral than the live!

Thank you all for the responses, very much appreciated.

To date, I have contacted Scottish Power to ensure that there was no fault at their end, this was confirmed as there are no faults! I have managed to get a hold of the electrician in question however he informed me that the wiring of the oven was done by his workmate. I told him that I am not looking for a blame game but to rectify the problem and safely and then worry about the financial impact(s). I will report the result should we ever find one....!!

Thanks again,
Brian
 
Last edited:
Try testing the voltage at oven between L-CPC. If that's 240V it's likely a poor neutral connection somewhere. If it's reading 150V then it's possibly a poor live connection.

Is the double oven on its own cct? It should be. And is there a local isolator in the kitchen for the oven; not mandatory but I would always fit one, and if there is then that would be a good place to test also.

Just to add. If the oven is not on its own cct, and you received no certificate of any kind I would start to question whether the original installer is competent and possibly be reluctant to have them back.

Also, have you put up any pictures or drilled holes etc in the vicinity of where the cables might be?
 
Last edited:
The oven in question "should" be fed from its own MCB from the board, I haven't noticed anything else switched off after isolating the MCB! The oven also has its own local isolator (I called it a switch in previous posts!)

Is it mandatory in Scotland to receive certification(s) for household electrical works?
 

Reply to Experiencing volt-drop within household in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
146
  • Sticky
  • Article
Thank you for getting in touch! Looking forward to use your services in the future! :)
Replies
3
Views
485
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
426

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
932
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
739

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top