Hello, could anybody explain why Main earth bonding is required and how it works in an event of a fault?
 
So the idea is to get R2 as low as possible, recommended as 0.05 Ohms, well according my 2391 lecturer.

This will be the concept of touch voltage that I don't know much about then.

Is that right?

Also I understand bonding being needed to create an equipotential zone and with a TN-C-S system it is important because of the risk of a lost or high resistance neutral joint but are there other instances where a TN-C-S earthing system floats above true earth?

I mean if my next door neighbour had an earth fault and seeing as I am connected to them via my neutral will the metal work in my house rise to the same potential as his assuming we are on the same phase?

Basically can anyone share any knowledge of when a TN-C-S earthing system would float above 0 volts?

Thanks.
 
Last edited:
So the idea is to get R2 as low as possible, recommended as 0.05 Ohms, well according my 2391 lecturer.

This will be the concept of touch voltage that I don't know much about then.

Is that right?

Also I understand bonding being needed to create an equipotential zone and with a TN-C-S system it is important because of the risk of a lost or high resistance neutral joint but are there other instances where a TN-C-S earthing system floats above true earth?

I mean if my next door neighbour had an earth fault and seeing as I am connected to them via my neutral will the metal work in my house rise to the same potential as his assuming we are on the same phase?

Basically can anyone share any knowledge of when a TN-C-S earthing system would float above 0 volts?

Thanks.

The voltage dropped across R2 will determine the PD, the PD may be quite high on stiff supply's.
 
Right I understand.

I thought originally you were talking about the potential difference under fault conditions between two exposed or extraneous conductive parts that had been bonded together.
 
Last edited:
If you have a long bonding cable to a pipe in the proximity of a far reaching metal clad socket at the end of a long radial the potential volt drop between the two under fault conditions could be quite high if the earth fault is right at the far reaching socket and you happen to touch both the pipe and socket simultaneously during the time of the fault.

Probability of this happening is probably :detective: very small but it could happen.

Supplementary bonding.

Can you supplementary bond an incoming metal pipe to a distant metal clad socket, is it a good idea?

Thanks.
 
Last edited:
Is it simple. If all the bonded metallic parts within simultaneous touching distance are at the same potential, you don't get a shock in the event of an earth fault, or close potential, and in theory you don't get time to die before the protective device cuts in. So when they say it reduces the magnitude, the magnitude is the difference between two extraineous metallic parts.

Earthing reduces the duration, a good earth means more current flows and so the protective device trips sooner.

Bonding is joined to earthing because it provides a combination of the two, pulling the touch voltages down to earth potentials and providing parallel paths to expedite tripping.

Sup bonding where required is not necessarily connected back to the met directly, but should be connected to the CPCs.

These do have downsides of course! See earth free zones, etc.
 
Last edited:

Reply to explanation of main earth bonding? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
562
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
936

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
779
loz2754
L
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top