Hello, could anybody explain why Main earth bonding is required and how it works in an event of a fault?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss explanation of main earth bonding? in the Australia area at ElectriciansForums.net
There may be a substantial potential difference.
There may be a substantial potential difference.
As above...please explain how there can be a substantial PD between CP's and ECP's when main bonding has been carried out.
So the idea is to get R2 as low as possible, recommended as 0.05 Ohms, well according my 2391 lecturer.
This will be the concept of touch voltage that I don't know much about then.
Is that right?
Also I understand bonding being needed to create an equipotential zone and with a TN-C-S system it is important because of the risk of a lost or high resistance neutral joint but are there other instances where a TN-C-S earthing system floats above true earth?
I mean if my next door neighbour had an earth fault and seeing as I am connected to them via my neutral will the metal work in my house rise to the same potential as his assuming we are on the same phase?
Basically can anyone share any knowledge of when a TN-C-S earthing system would float above 0 volts?
Thanks.
The voltage dropped across R2 will determine the PD, the PD may be quite high on stiff supply's.
Right I understand.
I thought originally you were talking about the potential touch voltage under fault conditions between two exposed or extraneous conductive parts that had been bonded together.
grossly undersized cpc compared to 0.1ohm for live conductor?