Hi
factory unit with 800 amp supply 95 mm main earth and 50 mm main bonds
portakabin has been delivered as a permanent addition
wired on 10 mm 3 core swa and 32 a commando plugs
there is a water supply and metal parts.

am I right in saying that it will need to be put on a stake as the main earth and bonds are so big.

Thanks mark
 
Not again . . . . . I see more arguments, and quoting of regulations that have yet to appear in the books I read :90:. It's probably sat on terra-firma anyway.

It's personal choice Mark,

Export PME with bonding conductors, or 'TT' it with RCD etc. Both have pro's, both have con's.

Regards

Billy
 
Sorry Mark I see where your coming from mate, your saying that your sizing your bonding conductor to the size of the neutral of the supplier, so as your bond is 50mm then the supply neutral must be 150mm+ and table 54.8

In your case though mate your Kabin is not a PME, as your not allowed a PME system inside your installation, so in all intent and purposes you have a PME that at origin as been converted into a TN-S inside the installation
 
Sorry Mark I see where your coming from mate, your saying that your sizing your bonding conductor to the size of the neutral of the supplier, so as your bond is 50mm then the supply neutral must be 150mm+ and table 54.8

In your case though mate your Kabin is not a PME, as your not allowed a PME system inside your installation, so in all intent and purposes you have a PME that at origin as been converted into a TN-S inside the installation


yep agree with 1st bit

not sure i follow what you mean on 2nd bit please can you clarify thanks
 

Reply to Export pme to portakabin in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

In Theory that’s a good argument but if you will be adding or moving switches or sockets or adding lights you’ll more than likely end up needing a...
Replies
7
Views
462
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top