Exporting PME to garage | on ElectriciansForums
Guest viewing is limited
Discuss Exporting PME to garage in the Australia area at ElectriciansForums.net
P
peteelecs
Please canyou help I am a bit confused about the earthing to a shed if the house is PME can I just run an earth from the MET to the shed or can I only do this if house is TNS.How do i get earth to shed if its PME hope this doesnt sound to confusing any suggestions would be appreciated
No difference between TN-S and TN-C-S (PME) once it's in the house in that respect. Separate neutral and earth once you're past the service head, whatever the supply may be.
Simon.
PME earthing should only be exported to buildings that are suitable as a seperate equipotential zone, if the building is suitable then an equipotential bonding conductor must be run equal to or larger csa to the one in the house and in any case a minimum of 10mmsq
Risks associated with sheds/garages are wet concrete floors and perhaps external metal cladding, for these reasons it is usual to create a segregated TT installation in the shed/garage,
PME can be used for earthing the sub main which is then segregated from the TT installation either by cutting back the armour or terminating in an insulated box, if you use this method the CCU in the garage must be all insulated
For the Zillionth trillionth time there are no regulations preventing the TNCS earthing system being used for an outbuilding.If there are extraneous conductive parts in the outbuilding requiring main bonding then you must run that bonding back to the MET,which means a TT is more sense....if there are no parts requiring main bonding then use the TNCS earth as for any other install....or if you prefer waste your time and money providing a totally unecessary separated earth.
But everyone isnt as key'd up on the regs such as joe blogs and doesnt know about bonding do they ? just a thought if you TT then their cover'd either way just in case thay add something to the structure !
Unusual to get the correct 'exporting pme' answer in just 9 posts :)
cant see the relevance.....the 'added' extraneous conductive part would need bonding even if it was TT....just the method of bonding would be different.
I know theres no requirements of TT in the brb its what i always do as said its personal pref only although the DNO might have a different view !
Reply to Exporting PME to garage in the Australia area at ElectriciansForums.net
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Now had panels for over a year, and still no payment for export, made application to British Gas on their forms, but they say wrong format, it...
Recommended Sponsor News
Hi everyone,