P

peteelecs

Please canyou help I am a bit confused about the earthing to a shed if the house is PME can I just run an earth from the MET to the shed or can I only do this if house is TNS.How do i get earth to shed if its PME hope this doesnt sound to confusing any suggestions would be appreciated
 
A garage will prob have a concrete floor then an issue is that the garage may be damp, have incoming services etc.
In which case you would not export a PME/TN-C-S house earth from the house, you would make the garage a TT install with earth rod

You are right to point out the damp floor situation which was known as an area of increased risk in my days as an installations inspector, what has not been mentioned so far on this long discussion is that the electrician has now been duckshoved the legal responsibility of using pme safely since the demise of the inspector, I say legal as it is the ESQCR who impose the pme regs and lets not forget that this is statutory document which every contractor should be aware of and possibly one that could be used against him/her as a duty holder
 
You are right to point out the damp floor situation which was known as an area of increased risk in my days as an installations inspector, what has not been mentioned so far on this long discussion is that the electrician has now been duckshoved the legal responsibility of using pme safely since the demise of the inspector, I say legal as it is the ESQCR who impose the pme regs and lets not forget that this is statutory document which every contractor should be aware of and possibly one that could be used against him/her as a duty holder

In the kind of domestic situation discussed here the key document is bs 7671.....as long as the installing electrician complies with that he has met his responsibilities.
 
hi everybody can i clear a few points up a friend has asked me to wire up his garage/workshop . i have had a look over the job which i was going to install a metal clad db . reason being so i can gland the armoured in and metal clad sockets for mechincal protection and the feed with a 3core swa cable from the db in the house which is not rcd protected but i can fit a rcbbo to hager db to protect the cable and all the circuits the garage construction is breeze block and gurder its 10meters from the house its more like a workshop to be honest is my method wrong ? oh yes the house earthing sytem is pme


thanks james
 
hi everybody can i clear a few points up a friend has asked me to wire up his garage/workshop . i have had a look over the job which i was going to install a metal clad db . reason being so i can gland the armoured in and metal clad sockets for mechincal protection and the feed with a 3core swa cable from the db in the house which is not rcd protected but i can fit a rcbbo to hager db to protect the cable and all the circuits the garage construction is breeze block and gurder its 10meters from the house its more like a workshop to be honest is my method wrong ? oh yes the house earthing sytem is pme

thanks james

You don't need to protect the distribution cable to the garage with an rcd as it is already has mechanical protection
, just use a submain with an rcd in.
 
ok thanks for that i just thought it would be easier to protect to whole thing from the house as i need a breaker for it and the just fit a dp mian switch at the garage db, and mcbs but can i use a metal clad db and sockets with a pme earthing system and the breeze block building with gurder type construction ?????????????????????
 
no probs there mate does that need to be a seperate earth back to the main earth terminal 10m/2 or can a spare core be used within the armoured if say a 4 core was used what about pme being used to earth a out building
 
no probs there mate does that need to be a seperate earth back to the main earth terminal 10m/2 or can a spare core be used within the armoured if say a 4 core was used what about pme being used to earth a out building


If you use the suppliers earth, your distribution circuit will have to be sized as a combined CPC and main protective bonding conductor and sometimes this is a better reason for making an outbuilding a TT system rather than worrying about this 'exporting PME' stuff.

The minimum CSA will be 10mm from table 54.8
 
hi thanks again for the replysi have some 4 core 10mm swa that i was going to use would i still need to run a seperate 10mm earth into there aswell ? or can i use a spare core ? i also have already bought the metal clad db is this ok to use still with a imported pme system ? and the garage/unit has a water supply via a plastic supply from the house mdpe ? blue pipe then 1 meter of copper with a tap on the end :confused::confused:
 
hi thanks again for the replysi have some 4 core 10mm swa that i was going to use would i still need to run a seperate 10mm earth into there aswell ? or can i use a spare core ? i also have already bought the metal clad db is this ok to use still with a imported pme system ? and the garage/unit has a water supply via a plastic supply from the house mdpe ? blue pipe then 1 meter of copper with a tap on the end :confused::confused:

I don't think it's best to use a metal clad db. If you get any earthing problems or future upgrades of the structure, you may find you'll have to TT the structure and therefore it would be against regs to use a metal one.
Shouldn't need to bond the water with plastic incoming. But this is notifiable work.
 
Hi yes guys thanks I know it notifable work i have my nvq3 and 17th edition I work for a jib firm but it's all industrail stuff im going to get my part p
berfore this job is done but just want to know what the yes and nos are
 
I don't think it's best to use a metal clad db. If you get any earthing problems or future upgrades of the structure, you may find you'll have to TT the structure and therefore it would be against regs to use a metal one.
Shouldn't need to bond the water with plastic incoming. But this is notifiable work.

What reg are you thinking of there or are you just talking about the possibility of the 'new' TT being connected to the original CU and the need to de-link them?
 

Reply to Exporting PME to garage in the Australia area at ElectriciansForums.net

Similar threads

  • Question
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Replies
8
Views
699
Now had panels for over a year, and still no payment for export, made application to British Gas on their forms, but they say wrong format, it...
Replies
5
Views
771

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top