Hi all this is my first post on here and any help would be great this question is starting to do my head in and Ive looked through loads of previous posts as I know its been covered before. I hope I have given enough information and explained it correctly.
I have a 95mm pme supply to a control panel, which has a back up generator. The generator cabin has a consumer unit (with lights, sockets, heaters all protected by a 30 MA trip and MCBs) which is supplied from the pme fed control panel (exporting pme). The generator casing is earthed via a flat copper bar (40mm x 5mm) which goes under ground. The oil pipes supplying the fuel tank are secured onto this copper bar with metal and are therefore earthed. Should the oil line have a 35mm main earth bond from the pme main earthing terminal. The copper earth bar is not connected to the consumer unit.
As i said any help on this would be great and if i am seeing a problem thats not there please let me know.
I have a 95mm pme supply to a control panel, which has a back up generator. The generator cabin has a consumer unit (with lights, sockets, heaters all protected by a 30 MA trip and MCBs) which is supplied from the pme fed control panel (exporting pme). The generator casing is earthed via a flat copper bar (40mm x 5mm) which goes under ground. The oil pipes supplying the fuel tank are secured onto this copper bar with metal and are therefore earthed. Should the oil line have a 35mm main earth bond from the pme main earthing terminal. The copper earth bar is not connected to the consumer unit.