if an existing ring main was extended by 2mtr (in kitchen ) is a cert.required ? and which one mwc or eic
 
Of course it does. The circuits been altered hasn't it Only way to ensure that the alteration complies and the circuit is safe to use is by testing and issuing MWC.

And aren't kitchens classed as special locations?
 
Not a special location but it is notifiable work. I've been caught out on here by this, I thought they were a special location until Tel bet me they wern't.
A large slice of humble pie was served to me:)

You are both correct. They are a special location in the building regs, but not the electrical regs.
 
Three areas in domestic installations require special attention
Bathrooms
Kitchens
Outdoors

It baffles me that Bathrooms and outdoors are regarded as 'special locations' and kitchens are not; the building regulations recognize it but BS7671 does not. Although back in the 15th ed. Kitchens were considered by BS7671 as a location of significance, but in the 16th ed lost their 'classification' and then it kicked off again when an MPs daughter was electrocuted in the kitchen.

Somebody knows why but it hasn't filtered down, as yet....
 
if an existing ring main was extended by 2mtr (in kitchen ) is a cert.required ? and which one mwc or eic


If the circuit is protected by a RCD then a MWC will do, if you need to add RCD or RCBO then it may make sense to do a EIC, especially if you're upgrading or adding bonding at the same time.
 
Three areas in domestic installations require special attention
Bathrooms
Kitchens
Outdoors

It baffles me that Bathrooms and outdoors are regarded as 'special locations' and kitchens are not; the building regulations recognize it but BS7671 does not. Although back in the 15th ed. Kitchens were considered by BS7671 as a location of significance, but in the 16th ed lost their 'classification' and then it kicked off again when an MPs daughter was electrocuted in the kitchen.

Somebody knows why but it hasn't filtered down, as yet....

Think Ack you will find that "outdoors" as an entity is also not a special location in the BS 7671-2008. And I would not be suprised if very soon sections 701/702 will also loose their special location tags.
 

Reply to ext. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
166
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Outside socket… ok. But you say the fcu for boiler is beside the outside socket… is the boiler outside too? FCU’s have an IN and an OUT… the OUT...
Replies
2
Views
241
Unless the circuit is new or has recently been tested/certified by a.n.other, I'm not sure how you prove the circuit is 'safe' to connect to...
Replies
1
Views
372

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top