Location
London
I was doing EICR on Saturday on the rented flat and apart from other issues I found that The Main Earth it has been extended with connector block so to reach the earth bar.(as to short)
The main earth it 6mm,and its the DB been upgraded by electrician 3 years ago.
What code would you give to extended main earth on connector, for EICR?
With the cable been short to reach only the DB but not the earth bar,can this been done without replacing the main earth on short term? need to damage the walls to get new earth cable,(having an MET out of CU is not option as cable too short )
On long term looking to change the CU and supply cable as supply is 16mm with 6mm main Earth.The distance from the meter to CU is about 5m,and tails allow only 3m,there is metal trunking used by existing supply
 
Hi
Not fixed,30A rated connectivity terminal strip,but what code would you give?

[ElectriciansForums.net] Extended main Earth on connector block
 
I’d just crimp and heat shrink it tbh. I know EICRs are not supposed to include remedials, but.....
I'd like to but at worst it's a C3 and if started correcting C3s id get my boss and his customer asking why I'm wasting there time doing things that aren't required, in their opinion.
 
There will be two camps on this, those that think okay and those who do not, I am the latter as I find unfixed block connectors a poor solution for conductor connections.
 

Reply to Extended main Earth on connector block in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
816
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top