extending 6mm cables for cookers | on ElectriciansForums

Discuss extending 6mm cables for cookers in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

R

rdelectrical

hi a landlord asked me after eicr test which picked up the cooker switch was directly over the hob meaning needed moving he asked if ok to join the cable in the ceiling using a proper junction box and re directing the cable i advised wasnt the best but given its a cottage with mostly stone floors except the kitchen running a new cable the full length of the cottage as a major job i suppose could be done then the property company i was there on behalf started to be funny about paying my bills so have pulled this as a breach of the 17th edition is this correct thanks for any advice
 
hi a landlord asked me after eicr test which picked up the cooker switch was directly over the hob meaning needed moving he asked if ok to join the cable in the ceiling using a proper junction box and re directing the cable i advised wasnt the best but given its a cottage with mostly stone floors except the kitchen running a new cable the full length of the cottage as a major job i suppose could be done then the property company i was there on behalf started to be funny about paying my bills so have pulled this as a breach of the 17th edition is this correct thanks for any advice

A MF box in the ceiling void, yes. A standard JB, no. It has to be accessible for inspection.

It's either against the Regs or it's not. It's not against the Regs because someone doesn't pay you. That's not really what the Regs are for!:uhoh2:
 
If you can access the JB afterwards its fine.. For example if its under a floor board that you have removed then just screw the floor board back down.. ITS ACCESSABLE then the next electrician can just unscrew floorboard job done..

If you cant access the joint when all work is finished then you need Maintenance Free ones
 
As long as the joint is electrically and mechanically sound and you get acces to the box then there is not a regulation to say no you cannot do that
 
many thanks guys your comments are what i thought the lanlord was ok with this as would be accessable from above its just the property company trying to pull my work the installation was tt i measured the rod found it to be 225 ohms i deemed not stable and should be rectified the property company bod who isnt a spark used another spark who converted it they now saying there was pme block which there was not as it is tt
and i was bigging the job up i hear conflicting things about converting tt to tncs by linking my friend says ok as long as you inform the electricity supplier and ze is ok whats your thoughts on this guys oh and be ware property companies seems there are folk wanting to shaft you at every turn
 
many thanks guys your comments are what i thought the lanlord was ok with this as would be accessable from above its just the property company trying to pull my work the installation was tt i measured the rod found it to be 225 ohms i deemed not stable and should be rectified the property company bod who isnt a spark used another spark who converted it they now saying there was pme block which there was not as it is tt
and i was bigging the job up i hear conflicting things about converting tt to tncs by linking my friend says ok as long as you inform the electricity supplier and ze is ok whats your thoughts on this guys oh and be ware property companies seems there are folk wanting to shaft you at every turn

You are not allowed to convert tt to a tncs supply. This must be done by your network operator and is usually free.
 
Just because the Ze is OK you cannot assume the system is suitable for TNCS. The only way is to call the distribution company to check whether or not the distribution system is PME. They will either check their plans and or send someone out and give you the definitive answer and it doesn't cost anything.
 
You are not allowed to convert tt to a tncs supply. This must be done by your network operator and is usually free.

You'd be amazed how many I see on I&T's where sparks have just put the earth into the neutral henley block! The DNO would likely take action if they found anyone doing it without permission, certain conditions have to be met (staked poles etc.) and I know for a fact in my area, there plenty of places which aren't PME ready
 
There you go rdelectrical, no conflicting views. It is illegal for an an electrician to attempt to convert any TT to a TNC-S system, and any electrician worth his salt should know this!
 
guys each and everyone of you are legends i remembered after the post a conversation with my niceic local guy he said the same things hence i was wanting to change the rod i knew i was right many thanks guys
 
cheers pal this property guy a right piece of work he trying to pull everything ive done cos owes a grand he even tried to quote safety on a job i was fault finding and did no work then this eicr test the fault finding was heating the cylinder stat was in parrellell with the room stat he saying it was the zone valve on the s plan which it wasnt so not wanting to pay
im just trying to do the job properly and you come up against these people isnt there a **** list we can put em on dont know what to do about the linking tt as this would shaft the other electrician
 

Reply to extending 6mm cables for cookers in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
411
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
887

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top