What do people tend to use as a connector when extending the ring, and the terminations are carried out in a knock out box? Push in wagos are rated at 24A, or the lever type at 32A.
I think (please correct me) 2.5mm enclosed in plaster (ref method C) has a CCC of 27A, so the push in wago would not be suitable at 24A. The lever type at 32A would be suitable in terms of CCC as least, but would it be the best tool for the job?
I've read some people crimp the two cables together, and I've seen others use chocolate blocks.
I think crimping would be the best (smallest size and most secure), but the red butt crimps were rated at 19A and the blue butt crimp at 27A (so I'm thinking as this matches the CCC of the cable it can be used).
Sorry, this turned in to a bit of a long winded post about not much, but would appreciate your thoughts/advice.