Hi I've to extend the dual immersion wiring both sides , fixed wiring to switch and immersion flex
Usually when extending these loads I double both ends of the wires back and insert wires in the same side and tighten them both under 2 screws. I always assumed this was a better connection than shoving a wire in either side under 1 screw each.
Prefer not to use wagos but just wondered thoughts on this as I've been caught out with an overheated connection on an old job and don't want same happening again
Tia
Usually when extending these loads I double both ends of the wires back and insert wires in the same side and tighten them both under 2 screws. I always assumed this was a better connection than shoving a wire in either side under 1 screw each.
Prefer not to use wagos but just wondered thoughts on this as I've been caught out with an overheated connection on an old job and don't want same happening again
Tia