That won't be waterproof will it? It rains on campsites.

Hookup leads for campsites are generally quite long as tents are often not next to the site hookup sockets.

Changing the plug on your cable reel should be OK. Just be sure the reel end remains inside the tent and is fully unwound.
 
Combination of both above points, ie: Long lead with Commando plug on one end and 13A socket on other end - this keeps the 13A fuse protection in place. Then a standard 4 way extension adaptor plugged in to this inside the tent - this keeps water off the plug/socket.
 
Strictly speaking, the OP's plan is not correct. The cable of a domestic extension lead will at the most be 1.25mm², which is rated for a maximum of 13A fully unrolled and should be protected by a 13A fuse. The protection on the 16A socket outlet may be 16 or 20A, so it would be possible to overload the cable if it has multiple 13A sockets as the load may be shared by more than one 13A fuse at the reel end.

In practice it's unlikely to be a problem, but when added to the fact that the cable is neither arctic grade or tough rubber, it is less than ideal to repurpose a multi-socket domestic extension in this way. Note that the thermal cutouts included in some reels are primarily to save the cable from melting into a solid lump if misused, and are not a good substitute for correct fusing at the plug end.

Personally I would prefer a fully rated 2.5mm² tough rubber 16A extension, converted to 13A at the load end.
 
Strictly speaking, the OP's plan is not correct. The cable of a domestic extension lead will at the most be 1.25mm², which is rated for a maximum of 13A fully unrolled and should be protected by a 13A fuse. The protection on the 16A socket outlet may be 16 or 20A, so it would be possible to overload the cable if it has multiple 13A sockets as the load may be shared by more than one 13A fuse at the reel end.

In practice it's unlikely to be a problem, but when added to the fact that the cable is neither arctic grade or tough rubber, it is less than ideal to repurpose a multi-socket domestic extension in this way. Note that the thermal cutouts included in some reels are primarily to save the cable from melting into a solid lump if misused, and are not a good substitute for correct fusing at the plug end.

Personally I would prefer a fully rated 2.5mm² tough rubber 16A extension, converted to 13A at the load end.
Would that be the Plug, Plug Top or Plug Bottom Lucien?:rolleyes::D
 
Nope, just the plug end. An extension lead has a plug end and a socket end. A bell circuit has three ends including the transformer end and the push end.:wink:
 
If they offer a hook up point surely they would be the people to ask? I find it surprising they offer a hook up point for a tent? Are they not usually for a vehicle that has a point that is compatible with it.
 
Previous career path so I knows my stuff.
We offered tent pitches with 16a rcd protected hookups the same as for touring caravans.
I recommended ready made 16a lead long enough to reach tent, then a short 4 way adaptor with the 13a plug swapped for 16a- INSIDE the tent
Don’t go overloading it.
I’ve seen tents with halogen heaters, 500w floodlights and kettles/ hotplates plugged into them
 
I’ve seen tents with halogen heaters, 500w floodlights and kettles/ hotplates plugged into them

That’s not “proper” camping! Shouldn’t have electric, should only have gas primus stoves, and a gas lantern.....that’s part of the fun!
 
That’s not “proper” camping! Shouldn’t have electric, should only have gas primus stoves, and a gas lantern.....that’s part of the fun!
gas for camping? luxury. a meths burner and candles was all we had in winter on the Brecon Beacons.
 

Reply to Extension lead (camping site) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
894

Similar threads

It's a room where someone sleeps, so it's a bedroom. Minimum standards were set in the Parker Morris report in around 1963. Anything built after...
Replies
5
Views
1K
Need to crack on to get most from this year :cool: BTW if you are thinking about adding to the strings later, i.e. add more panels to existing...
Replies
6
Views
932

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top