Hi all,

I can't understand why but I always get a small (minimum 0.06mA) earth leakage reading on extension leads (even without surge protection).

Is this normal?

If it is, please could someone explain how earth leakage occurs on a simple extension lead?

Thanks
 
How are you measuring it?

if it is a long lead, there could be some inductive coupling between the cores as they are running parallel to each other
 
This is likely capacitive leakage. For example, one metre cable with 30pF between line and earth conductors would have a capacitive reactance of 1/(2*pi*50*30Exp-12) = approx 100MΩ. At 230V a 25m cable will leak 25*230/1Exp8=0.058mA. This is a genuine current that leaks across all cables all the time they are energised but because it is reactive it doesn't register as power consumption on a watt-hour meter. It's also pretty small, and off the bottom of the scale of some testers; mine only displays <0.1mA when this low.
 
Last edited:
Are tutor taught us all that malarkey and all made sense at the time, as of today its pie to the power of 12 up in the sky..

Excellent that you so fluent.
 

Reply to extension leads - earth leakage in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

out of interest UK, how do you know what kit is connected?
Replies
8
Views
1K
  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top