I am currently P.A.Testing an extension lead.I have classed it as class 1 equipment beacuse of the protective conductor and obviously extension leads need a protective conductor as they could be supplying class 1 equipment and appliances which if it did not have one and there was a fault in the appliance used there would be no protection form electric shock.The problem is the Extension lead is portable and has a handle.This handle is metal and i dont think the earth is connected to it probably due to basic insulation.So it kind of makes it a class 2 doesnt it?
So how can i do an Earth continuity test onit then?
Another thing - i was insulation resistance testing one of my grinders and it gave a insulation value of 1ohm.In the code of practice for in-service inspection and testing of electrical equipment it gives you values of what aplliances should be:
So how can i do an Earth continuity test onit then?
Another thing - i was insulation resistance testing one of my grinders and it gave a insulation value of 1ohm.In the code of practice for in-service inspection and testing of electrical equipment it gives you values of what aplliances should be:
- Class 1 heating and cooking equipment =0.3 M ohm
- All other Class 1 equipment =1.0 M ohm
- Class 2 equipment =2.0 M ohm
- Class 3 equipment =250 K ohm