Hi there all,

I have a property and I have noticed the following wiring (please see below) in one of the rooms in the house.

It looks like the ring circuit has been extended.
A single 2.5mm Twin + Earth cable (in red) is providing power from the consumer unit which feeds a chain of electrical sockets via a junction box which returns back to the junction box.

Every socket has two cables (feed in & feed out). To my understanding given that each socket has two cables (provided continuity is sound) the load would be shared between cables to ensure no one cable is overloaded.

However couldnt the single cable giving power from the consumer unit be overloaded or would that be fine given that the power returns back via the junction box?
Im guessing the single cable coming from the MCB with a 32a breaker could be overloaded right?

I know this is far from satifactory under regulations but my first concern is safety.
 

Attachments

  • socket diagram.png
    socket diagram.png
    53.1 KB · Views: 2,615
However couldnt the single cable giving power from the consumer unit be overloaded
Yes.

or would that be fine given that the power returns back via the junction box?
No.

Im guessing the single cable coming from the MCB with a 32a breaker could be overloaded right?
Yes - it needs to be rated to at least 32A, and 2.5mm² isn't, no matter how it's installed.

I know this is far from satifactory under regulations but my first concern is safety.
The circuit topology is what's known as a "lollipop", and whilst it is unusual, and can annoy electricians who have to test it, if you get the cable from the JB replaced with one rated ≥ 32A it won't be unsafe and won't contravene any regulations.

But if you're going to have that done, why not just make it a ring all the way?

What sort of JB is it? Where is it? Could a second one go there? How far is it from there to the first/last sockets? What's access to those cable routes like?
 
Yes.


No.


Yes - it needs to be rated to at least 32A, and 2.5mm² isn't, no matter how it's installed.


The circuit topology is what's known as a "lollipop", and whilst it is unusual, and can annoy electricians who have to test it, if you get the cable from the JB replaced with one rated ≥ 32A it won't be unsafe and won't contravene any regulations.

But if you're going to have that done, why not just make it a ring all the way?

What sort of JB is it? Where is it? Could a second one go there? How far is it from there to the first/last sockets? What's access to those cable routes like?
Interesting. I didn’t realise this was called a “lollipop”.

The cable from the consumer unit is under the floorboards upstairs.
The JB is one of those wago JBs with the 222 wago connector blocks.

I’m not sure if I can find the cable that returns back to the Consumer unit to make this ring circuit correct again.
I would otherwise use a junction box to connect to the last socket on this “lollipop” to rectify.

Thanks for your help.
I really appreciate your response.
 
Hi there all,

I have a property and I have noticed the following wiring (please see below) in one of the rooms in the house.

It looks like the ring circuit has been extended.
A single 2.5mm Twin + Earth cable (in red) is providing power from the consumer unit which feeds a chain of electrical sockets via a junction box which returns back to the junction box.

Every socket has two cables (feed in & feed out). To my understanding given that each socket has two cables (provided continuity is sound) the load would be shared between cables to ensure no one cable is overloaded.

However couldnt the single cable giving power from the consumer unit be overloaded or would that be fine given that the power returns back via the junction box?
Im guessing the single cable coming from the MCB with a 32a breaker could be overloaded right?

I know this is far from satifactory under regulations but my first concern is safety.
No,if I understand the your layout any ring final cct starts at the consumer unit, connects into various sockets
then returns to the cu,so 2 cables in the mcb.Sounds like you have a daisy chain of sockets without a return so chance of overloading the cable.A solution could be to fit a fused spur at the start of the chain,remembering no more than 13A could be drawn on the chain of sockets.Volt drop and other factors
would also have to be considered.
Regards,S
 
If your red "power from the consumer unit" cable is 2.5mm then the MCB should be 20A, as 32A is too much for overload protection.

If it was 4mm (without much thermal insulation) or 6mm (as commonly for cooker feeds) then you could get away with a 32A MCB no problems.
 
If your red "power from the consumer unit" cable is 2.5mm then the MCB should be 20A, as 32A is too much for overload protection.

If it was 4mm (without much thermal insulation) or 6mm (as commonly for cooker feeds) then you could get away with a 32A MCB no problems.
I might be mis interpreting this but as far as I’m aware you are allowed to (spur off) from a ring final circuit mcb 32A at mcb providing it powers one socket outlet. The regs do show a nice picture diagram of this. It is no different to spurring off a socket outlet connected directly to the ring final. Hope this helps
 
No,if I understand the your layout any ring final cct starts at the consumer unit, connects into various sockets
then returns to the cu,so 2 cables in the mcb.Sounds like you have a daisy chain of sockets without a return
I took it that the red cable is a 3rd one from the breaker....

I might be mis interpreting this but as far as I’m aware you are allowed to (spur off) from a ring final circuit mcb 32A at mcb providing it powers one socket outlet. The regs do show a nice picture diagram of this. It is no different to spurring off a socket outlet connected directly to the ring final. Hope this helps
It's very different in that none of the current for the "spur" flows in the ring final, so none of the concerns about overloading a section of that would apply.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Birmingham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
Extension of ring final circuit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
raj_121,
Last reply from
Soi disant,
Replies
8
Views
8,236

Advert

Back
Top