Hi just looking for some advice,
Extension has been built onto the side of a
house and they are putting in a separate consumer unit (just for the extension) and it will be fed off the existing consumer unit with a 16mm T&E. Distance between the 2 boards approx 6 metres. It’s a big enough extension so that’s why they would like their own board.
The existing board mains fuse is 63A.
Would you recommend my new tails feeding the new CU be terminated in with the incoming supply (meter supply into the existing CU ) or come of the load side of the fuse in the existing CU?
Or any other options?
Thanks in advance
 
I'd suggest taking the 16mm from an additional device in the existing CU would be a very poor design as there's a chance of overloading. You need to split the tails after the meter using 100 amp single pole blocks and connect a 63amp metalclad switch fuse for your new 16mm to the extension CU. But there's another consideration as the sub-main may well need additional 30ma RCD protection depending on how it's been installed and the route.
 
I'd suggest taking the 16mm from an additional device in the existing CU would be a very poor design as there's a chance of overloading. You need to split the tails after the meter using 100 amp single pole blocks and connect a 63amp metalclad switch fuse for your new 16mm to the extension CU. But there's another consideration as the sub-main may well need additional 30ma RCD protection depending on how it's been installed and the route.
last bit.... he could use SWA, to eliminate RCD.
 
Feeding the 2nd CU from the first CU would mean it is off a MCB (possibly also RCD protected) and likely to have poor selectivity with the protection in the 2nd CU itself.

Feeding it from a switched-fuse off the (split) incoming tails would give the best selectivity, but the remaining question would be if the T&E needs RCD protection. I have no idea under what conditions the ROI regs demand it, but assuming they are broadly comparable to our 18th then either the T&E needs physical protection and/or careful routing to be > 50mm deep in any walls, etc.

Or go for the the safer and more professional option is to use some SWA with proper glands to terminate the armour at the switch-fuse and at the 2nd CU and not require RCD protection (assuming TN, and not a TT supply, of course, that is a whole other can of worms).

Even if going down the T&E route you should really be using some matching glands for cable entry protection and physical support such as these:
 

Reply to Extension supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
Yeh that’s my thinking. I have to supply the box so can order a bigger 3 phase option to give myself a bit more room
Replies
3
Views
834
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
801

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top