external consumer unit... | on ElectriciansForums

Discuss external consumer unit... in the Australia area at ElectriciansForums.net

E

equinox

hi chaps, ive got to run an armoured cable down to a new consumer unit in an 'outbuilding'. on the comsumer, should i use an RCD incomer? on the diss board? Ive not done this sort of thing before so i assume i just come out of the diss board in the main building on a spare breaker and down to the new diss board. Also i have to run two armoured cables out to ponds, i assume these will have to be RCD protected as they are outside?

thanks chaps
 
hi chaps, ive got to run an armoured cable down to a new consumer unit in an 'outbuilding'. on the comsumer, should i use an RCD incomer? on the diss board? Ive not done this sort of thing before so i assume i just come out of the diss board in the main building on a spare breaker and down to the new diss board. Also i have to run two armoured cables out to ponds, i assume these will have to be RCD protected as they are outside?

thanks chaps
Can you not put a 63A isolator by the main CU feeding the outbuilding CU.Reason be if it trips in the outbuilding it will trip at the main CU,and then take your 2 SWA to the ponds:eek:They will have to be RCD protected if run outside
 
Last edited by a moderator:
so... if i was to put a 63A isolator next to the main board, then what A of breaker should be in the board, would it be a 63A breaker feeding the 63A Isolator and then down to the distribution unit?

Also any idea what mm2 of cable i should use to run the cable down in?

Thanks for the help chaps
 
Just to add if unless the swa is continuous in its length from main cu to outbuilding cu and not run from house cu in pvc to junction and terminated inside into the swa to say run underground or clipped etc outside then the distribution cable needs to be rcd protected.
With regards cable mm2 what length of run is it ? whats the max demand etc etc breaker/cable size etc is same old calcs as for all circuits.
 
Last edited by a moderator:
Equinox, it would be useful to all if you could supply more details - cable run lengths, likely loading & especially earthing system, as the exact type would impact on what you need to do (TN-C-S & exporting equipotential zone etc)

As for RCD protection, for many installs outside it isn`t a strict requirement, but i would consider it preferable in most cases regardless. Especially if ponds feature in the install. You mention a CU in outbuilding...can we assume that`ll be feeding s/o cct? If so, 30mA RCD will be required irrespective of cable types.

Also, if an RCD is required, discrimination between the devices needs to be achieved. You don`t say if the `spare` breaker is on the unprotected side of board (assuming split board?)

& to be sure you know, as this is a Special Location it`s notifiable under Part P ;)
 
Last edited by a moderator:

Reply to external consumer unit... in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
920
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
718
I would hazard a guess your electrician may be able to contact your DNO and have the switch swapped to a MFS very quickly..
Replies
13
Views
651

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top