Hi,

I'm updating our bathroom and I'm changing our extractor fan from a simple ceiling mounted one to a more powerful inline version (Blauberg) mounted in the loft.

The fan only had 2 wires - a black and a red.
It has an isolator switch outside the door in a twin switch plate shared with the lighting. (so 2 switches - the left for the fan and the right for the lights).
There is no timer on the current fan.

We are happy for the new fan to run in the same way - i.e. when the switch is on

The new fan however has 3 connections - Neutral (N), Live (L), Switched Live (LT).

I wired up as:
black to N (from the isolator switch this comes from a blue wire)
red to L (again its red to red in the isolator switch).

The fan doesn't work.

I attached photos of the twin switchplate with the isolator switch (on the left) and the top of the fan.
  • You see that the red and black cables I mentioned are 2 core
  • There is then a 3 core + earth running up from the same switch plate to the lighting to the ceiling rose which is now in the loft and accessible.

Can anyone help?


Many thanks,

Chris
 

Attachments

  • [ElectriciansForums.net] Extractor Fan (red and black wires only)
    1.jpg
    453.4 KB · Views: 93
  • [ElectriciansForums.net] Extractor Fan (red and black wires only)
    2.jpg
    254.5 KB · Views: 49
  • [ElectriciansForums.net] Extractor Fan (red and black wires only)
    3.jpg
    225 KB · Views: 68
Last edited by a moderator:
We can only guess here what is the feed to the switch, so someone with a voltage tester would have to clarify….

the 3 terminals in the fan are neutral…. Permanent live, which actually runs the fan and a switched live, this is normally joined to the light so the fan operates when the light goes on, and the permanent live runs on after the light is turned off.
It appears you have a live, switched live and neutral at this switch.
you may also have the same at the light….
 
Hi,

I'm updating our bathroom and I'm changing our extractor fan from a simple ceiling mounted one to a more powerful inline version (Blauberg) mounted in the loft.

The fan only had 2 wires - a black and a red.
It has an isolator switch outside the door in a twin switch plate shared with the lighting. (so 2 switches - the left for the fan and the right for the lights).
There is no timer on the current fan.

We are happy for the new fan to run in the same way - i.e. when the switch is on

The new fan however has 3 connections - Neutral (N), Live (L), Switched Live (LT).

I wired up as:
black to N (from the isolator switch this comes from a blue wire)
red to L (again its red to red in the isolator switch).

The fan doesn't work.

I attached photos of the twin switchplate with the isolator switch (on the left) and the top of the fan.
  • You see that the red and black cables I mentioned are 2 core
  • There is then a 3 core + earth running up from the same switch plate to the lighting to the ceiling rose which is now in the loft and accessible.

Can anyone help?


Many thanks,

Chris
If you put a wire link between switched live and live on the fan,it will work as before.
Regards,S
 

Reply to Extractor Fan (red and black wires only) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi all, first post, please be gentle ;) Iv been involved in a bathroom refurb, nothing major, moving a light fitting and switch. My problem came...
Replies
0
Views
200
  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top