uksparks
-
Hi,
something that cropped up yesterday on my assessment was that I'd done a load of work on a house and new CU etc.
the old boiler had been taken out and a new one fitted but the gas supply had not been put into the new boiler.
the old gas pipe was left where the old boiler was in a different part of the house.
i didn't bond the old pipe as it was about to be removed and a new one put in.
he said why have you not bonded the gas pipe?
i said it was about to be removed.
i said I have done an IR on it to the MET and it suggested it was not extraneous or already bonded somewhere so was not bothered as I felt it to be satisfactory.
he said what do you mean you have done an IR test in it?
so I explained it was less than 0.03M ohms, it was 0.00 as it happens, so it was less that 23,000 ohms. He said that it should be well over 1 meg ohm. I had to agree to disagree, I said yes but I'm proving it's not extraneous....
am am I right or am I being thick?
something that cropped up yesterday on my assessment was that I'd done a load of work on a house and new CU etc.
the old boiler had been taken out and a new one fitted but the gas supply had not been put into the new boiler.
the old gas pipe was left where the old boiler was in a different part of the house.
i didn't bond the old pipe as it was about to be removed and a new one put in.
he said why have you not bonded the gas pipe?
i said it was about to be removed.
i said I have done an IR on it to the MET and it suggested it was not extraneous or already bonded somewhere so was not bothered as I felt it to be satisfactory.
he said what do you mean you have done an IR test in it?
so I explained it was less than 0.03M ohms, it was 0.00 as it happens, so it was less that 23,000 ohms. He said that it should be well over 1 meg ohm. I had to agree to disagree, I said yes but I'm proving it's not extraneous....
am am I right or am I being thick?