In that case, if you are getting 0.5 ohms between socket CPC and floor then it must be bonded somewhere already.

Is he on about supplementary bonding between socket CPC and floor?

Running a main bond from stool to board would be strange.
 
In that case, if you are getting 0.5 ohms between socket CPC and floor then it must be bonded somewhere already.

Is he on about supplementary bonding between socket CPC and floor?

Running a main bond from stool to board would be strange.
its ridiculous, i have come across these floors before.

metal pedestals bolted to floor with metal covered wooden tiles ontop, usually covered with carpet tiles
 
Sorry I was nor clear, we was just taking measurements, no bonds were actually in place. The floor will get an earth via floor boxes.
However we was measuring continuity between wall socket cpc, and tile.
All extraneous earth's were measured.
From uni strut to tray work to trunking to ceiling grid to steelwork etc etc etc.
I was just trying to clarify if there was actually an regulation that stated these measurements should be below 0.05 ohms
 
Sorry I was nor clear, we was just taking measurements, no bonds were actually in place. The floor will get an earth via floor boxes.
However we was measuring continuity between wall socket cpc, and tile.
All extraneous earth's were measured.
From uni strut to tray work to trunking to ceiling grid to steelwork etc etc etc.
I was just trying to clarify if there was actually an regulation that stated these measurements should be below 0.05 ohms
it would be a lot lower from unistrut etc to it.

it will probably only have 2.5/4mm cpc at most.


there was so many glanded swa and steel in last plantroom the cpc reading was a lot lower than L-N because of parralel paths etc
 
How did the metal flooring grid become extraneous in the first place??

I think there is some confusion here between earthing and bonding. Earthing is generally required with metalwork that forms part of an electrical installation such as metal containment systems (conduit, trunking, tray etc) or where part of an electrical installation is integrated into a metal structure etc (such as in this case, these floor sockets in the metal flooring system)... Other building metalwork that brings an extraneous potential into a building is required to be main bonded. Other building metal work that is not extraneous (proven by testing >22k ohms) needs neither bonding or earthing in fact it could well be dangerous to do so!!
 
Thanks Engineer54. I knew I could rely on you.

The main bonds were indeed to the main steelwork, and ductwork.
A couple of low noise earth's were installed to the server room as would be expected.
It's just that the consultant was insisting on this low continuity reading between points.
Thus the original question.
 
As nobody can pull any regulation out, just guidance notes

A misunderstanding of the Guidance Notes at that. It is suggesting that would confirm continuity between two points. It is NOT suggesting that the resistance of the main protective bonding conductor should not exceed this.
 
A misunderstanding of the Guidance Notes at that. It is suggesting that would confirm continuity between two points. It is NOT suggesting that the resistance of the main protective bonding conductor should not exceed this.

Unless of course the contract electrical specification calls for this as a maximum value. Otherwise you are correct...
 
The 0.05 figure is just the value that is acceptable for a connection. So if you fit an earth clamp to a copper pipe, the value between the conductor connected to the clamp terminal and the pipe it's connected to should be no more than 0.05ohms. It's to confirm the connection is good. If you had a 70m run of 10sq.mm, it's not going to measure 0.05 ohms end to end is it.
 

Reply to Extraneous bonds values in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
731
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
972

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
347
Hi I need help with understand supplementary bonding. I know RCD is additional protection and in the even of the fault at leakage of 30mA, it...
Replies
0
Views
101

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top