With all the rush for landlord EICR's lately been getting few enquires and failed certs sent over to me to quote on remedials. Realise you need a greater grasp of regs and experience to do do eicr's on regular basis so not venturing out doing many of these myself at the moment but do find it surprising some of the failed inspections getting sent over to me. Been asked to quote on possibly changing spots or providing rcd protection to lighting circuit. Went to property today customer has 230v volt spots in property and as see in photo one above shower. Can someone correct me if seeing this wrong but even though spots are not on rcd they are 2.25m above floor so fall within zone 2. There is nothing on them suggesting their ip or fire rating but are the flush mounted type with glass seal so surely these provide at least the ip4x requirement needed and although in a block of flats the separation between floors is concrete so no requirement for fire rated fixtures? Thanks