A church near me has been tested as unsatisfactory with many recommendations, including 5 grade 1's.
Having not seen any of the installation as yet i've been asked to have a look at the schedules to advise on what work may need doing and if i could carry out any correcting actions to the installation myself.
It's an old church, the estimated age of the electrical installation is 40+ years there has been signs of various alterations/additions.
No previous records of testing were found to compare.
The 5 grade 1's are as follows;
1) Main bonding cable to gas and water is insufficient at only 2.5mm (10mm required) furthermore it is split, recommend seperate cables to each source or unslipt 10mm cable to service both.
2) Lightning conductor has been cut and needs repairing.
The other 3 grade 1's are to do with the circuits via the power board within the church.
1) 2 radial sockets are wired in 1.5mm MICC and protected by a B32 amp breaker.
2) 9 sockets are served on their own ring wired again in 1.5mm MICC again protected by a B32 amp breaker.
3) Heating controls serving 9 points are wired with a mixture of MICC and pvc cabling protected by a B20 amp breaker.
All above circuits are proteced by overrated fuses and their recommendation is to lower the fuse ratings to suffice.
I know MICC is the best type of cable for longevity out there and looking at the IR testing it could stay around for many years to come however a ring wired in 1.5mm. Surely that needs upgrading to at least 2.5mm? the radial with just 2 points should be ok in 1.5mm but needs a 16/20amp breaker rather than a 32amp thats currently protecting it, (bare in mind this is without looking at the job). As for the heating controls i wouldn't like to guess untill i look at the job but can't imagine it pulling anywhere near 20amps.
The church in size isn't all that great, somewhere in the region of 50m by 20m.
There's other lesser recommendations such as DB chart needs updating, cables need clipping etc.
I obviously need to view the job myself but seems to me like a lot of work needs doing to make this church anywhere near to todays standards.
Anyone out there who've tested and corrected any similar installations and any advice on the grade 1's above please?
Having not seen any of the installation as yet i've been asked to have a look at the schedules to advise on what work may need doing and if i could carry out any correcting actions to the installation myself.
It's an old church, the estimated age of the electrical installation is 40+ years there has been signs of various alterations/additions.
No previous records of testing were found to compare.
The 5 grade 1's are as follows;
1) Main bonding cable to gas and water is insufficient at only 2.5mm (10mm required) furthermore it is split, recommend seperate cables to each source or unslipt 10mm cable to service both.
2) Lightning conductor has been cut and needs repairing.
The other 3 grade 1's are to do with the circuits via the power board within the church.
1) 2 radial sockets are wired in 1.5mm MICC and protected by a B32 amp breaker.
2) 9 sockets are served on their own ring wired again in 1.5mm MICC again protected by a B32 amp breaker.
3) Heating controls serving 9 points are wired with a mixture of MICC and pvc cabling protected by a B20 amp breaker.
All above circuits are proteced by overrated fuses and their recommendation is to lower the fuse ratings to suffice.
I know MICC is the best type of cable for longevity out there and looking at the IR testing it could stay around for many years to come however a ring wired in 1.5mm. Surely that needs upgrading to at least 2.5mm? the radial with just 2 points should be ok in 1.5mm but needs a 16/20amp breaker rather than a 32amp thats currently protecting it, (bare in mind this is without looking at the job). As for the heating controls i wouldn't like to guess untill i look at the job but can't imagine it pulling anywhere near 20amps.
The church in size isn't all that great, somewhere in the region of 50m by 20m.
There's other lesser recommendations such as DB chart needs updating, cables need clipping etc.
I obviously need to view the job myself but seems to me like a lot of work needs doing to make this church anywhere near to todays standards.
Anyone out there who've tested and corrected any similar installations and any advice on the grade 1's above please?