It's the RC version of the Vestry
Whoever did this PIR appears to exude inexperience IMO my only other thought is his scheme is rewire the socket ring in PVC/PVC or Hi Tuf cable and weigh the 1.5 Pyro in
Why is it there seems to be a thing with some people that if an installation isn't up to the latest regs then it's unsafe
Or, he's not done much with MICC / old churches before and is therefore un-familiar with such situations.
In terms of "knowing" the older regs and stuff, that has to obviously come with years on the job and experiencing different situations as newer courses probably don't teach the older regs.
So if you aren't familiar, ask those who might (forums are geat for that (and risk getting flamed for not knowing)).
The point i was making, if he needs to change these existing 2.5mm, then he might as well change them to 10mm. Who knows what the next generation of bonding regulations might be...lol!! And if it is a TT installation, it could always be PME'd at a future date....
DB 1 - Power DB:-
Schedule:
cct 1: (Altar radial sockets) Wired in MICC 1.5mm live & cpc (14th Ed imp 1.29/1.94 21A/26A 1.5mm 25A), 2 points served, B32A fuse.
cct 3: (Organ supply) Wired in PVC cables in metallic trunking, 2.5mm lives, 1.5mm cpc (23A), B32A fuse.
cct 5: (Heating controls) Wired with mixture of PVC (19.5A) and MICC (25A)cables, 1.5mm live & cpc, 9 points served, B20A fuse.
CCCs are assuming ref method C, if not otherwise specified.
So cct1 2 points served? max 26A limited load?
Generally code 2 drop breaker to 20A
Cct2 assuming radial Code 2 drop breaker to 20A, what is the current draw from the organ, if less than 23A cable is protected and does not need overcurrent protection.
Cct 5 was OK with the original MICC but the introduction of PVC means should be 16A breaker code 2.
That's as I thought.thanks Richard, i'm yet to check the installation first hand, here are the reference methods;
cct's 1 and 5 are C, cct 3 is ref method B.
DB 1 - Power DB:-
CCCs are assuming ref method C, if not otherwise specified.
So cct1 2 points served? max 26A limited load?
Generally code 2 drop breaker to 20A
Cct2 assuming radial Code 2 drop breaker to 20A, what is the current draw from the organ, (if less than 23A cable is protected and does not need overcurrent protection.) - I don't understand this bit please expand.
Cct 5 was OK with the original MICC but the introduction of PVC means should be 16A breaker code 2.