Failed PIR on an old church | Page 2 | on ElectriciansForums

Discuss Failed PIR on an old church in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

DB 1 - Power DB:-


Schedule:


cct 1: (Altar radial sockets) Wired in MICC 1.5mm live & cpc (14th Ed imp 1.29/1.94 21A/26A 1.5mm 25A), 2 points served, B32A fuse.
cct 3: (Organ supply) Wired in PVC cables in metallic trunking, 2.5mm lives, 1.5mm cpc (23A), B32A fuse.
cct 5: (Heating controls) Wired with mixture of PVC (19.5A) and MICC (25A)cables, 1.5mm live & cpc, 9 points served, B20A fuse.

CCCs are assuming ref method C, if not otherwise specified.
So cct1 2 points served? max 26A limited load?
Generally code 2 drop breaker to 20A
Cct2 assuming radial Code 2 drop breaker to 20A, what is the current draw from the organ, if less than 23A cable is protected and does not need overcurrent protection.
Cct 5 was OK with the original MICC but the introduction of PVC means should be 16A breaker code 2.
 
DB 1 - Power DB:-


Schedule:


cct 1: (Altar radial sockets) Wired in MICC 1.5mm live & cpc (14th Ed imp 1.29/1.94 21A/26A 1.5mm 25A), 2 points served, B32A fuse.
cct 3: (Organ supply) Wired in PVC cables in metallic trunking, 2.5mm lives, 1.5mm cpc (23A), B32A fuse.
cct 5: (Heating controls) Wired with mixture of PVC (19.5A) and MICC (25A)cables, 1.5mm live & cpc, 9 points served, B20A fuse.

CCCs are assuming ref method C, if not otherwise specified.
So cct1 2 points served? max 26A limited load?
Generally code 2 drop breaker to 20A
Cct2 assuming radial Code 2 drop breaker to 20A, what is the current draw from the organ, if less than 23A cable is protected and does not need overcurrent protection.
Cct 5 was OK with the original MICC but the introduction of PVC means should be 16A breaker code 2.

thanks Richard, i'm yet to check the installation first hand, here are the reference methods;

cct's 1 and 5 are C, cct 3 is ref method B.
 
DB 1 - Power DB:-

CCCs are assuming ref method C, if not otherwise specified.
So cct1 2 points served? max 26A limited load?
Generally code 2 drop breaker to 20A
Cct2 assuming radial Code 2 drop breaker to 20A, what is the current draw from the organ, (if less than 23A cable is protected and does not need overcurrent protection.) - I don't understand this bit please expand.
Cct 5 was OK with the original MICC but the introduction of PVC means should be 16A breaker code 2.

So when i have a look at job tomorrow barring no suprises as per schedule i ought to recommend the preist gets fuses changed to 20A for cct 1, 20A for cct 3 and 16A for cct 5? To get 10mm bondong sorted. All these things i could possibly do myself for him.

What is your advice on the lightning conductor with regards to, is it part of the grading on a PIR? Some have said not and that is a seperate issue/test. A specialist contractor to repair, test and certify all in one?

Many thanks.
 
Obviously for both us and you at a distance we cannot truly tell what the situation is.
That said, changing the fuses (thought they were breakers) to the above values would be protecting the cables appropriately. You would need to review the actual circuits to ensure that there are no other problems, and in an earlier post (which we were to disregard) there was a ring circuit which would have complied so just check you are not unnecessarily reducing the breakers.
Upgrade the bonding to suitable levels.

For the lightning protection, I cannot really give suitable advice as I do not know, but a specialist would probably be a better bet than attempting something you do not know about.
 

Reply to Failed PIR on an old church in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
Received guidance from a logical soul on the Kawie Riders forum: Acc Fuse Block Power to BAT LOAD, install new cable from BAT LINE to AUX + (and)...
Replies
1
Views
303
  • Question
Will it work? Yes. Will the trailer burst into flames? No. But code allows a remote structure (trailer) to be powered with ONE circuit, which...
Replies
6
Views
1K
Good luck with your project and welcome to the forum
Replies
5
Views
1K
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
865
Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
359

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks