recently passed my 2391 and testing power cables on the motorways and A Roads. Came across this scenario last week.
3 core SWA cable has had Cpc cut and only line and neutral terminated, but cable is glanded and connected to the MET at both ends and I am getting a r1 r2 continuity reading when I drop the cable. Zs reading is within spec for protective device also but cable fails line-earth and neutral - earth on insulation resistance (0.5MOhm and 0.75MOhm). I isolated and locked off the circuit as the regs state that IR is a minimum of 1 meg.
Just been informed that I should have left the circuit on as the Zs is ok.
Just trying to clear things up as I am new to testing and want to do the right thing.
cheers!
recently passed my 2391 and testing power cables on the motorways and A Roads. Came across this scenario last week.
3 core SWA cable has had Cpc cut and only line and neutral terminated, but cable is glanded and connected to the MET at both ends and I am getting a r1 r2 continuity reading when I drop the cable. Zs reading is within spec for protective device also but cable fails line-earth and neutral - earth on insulation resistance (0.5MOhm and 0.75MOhm). I isolated and locked off the circuit as the regs state that IR is a minimum of 1 meg.
Just been informed that I should have left the circuit on as the Zs is ok.
Just trying to clear things up as I am new to testing and want to do the right thing.